07-19-2021 06:10 AM
We are running NXOS version 9.3.7 and are also experiencing this bug. Unlike what is listed in the description both of our power were showing as shutdown and were alerting in our NMS. The switch was online and operating without issue otherwise. Reseating of the power supplies has resolved the issue.
93180# show env power
Power Supply:
Voltage: 12 Volts
Power Actual Actual Total
Supply Model Output Input Capacity Status
(Watts ) (Watts ) (Watts )
------- ---------- --------------- ------ ---------- --------------------
1 NXA-PAC-500W-PE 0 W 0 W 0 W Shutdown
2 NXA-PAC-500W-PE 0 W 0 W 0 W Shutdown
Power Usage Summary:
--------------------
Power Supply redundancy mode (configured) PS-Redundant
Power Supply redundancy mode (operational) Non-Redundant
Total Power Capacity (based on configured mode) 0.00 W
Total Grid-A (first half of PS slots) Power Capacity 0.00 W
Total Grid-B (second half of PS slots) Power Capacity 0.00 W
Total Power of all Inputs (cumulative) 0.00 W
Total Power Output (actual draw) 0.00 W
Total Power Input (actual draw) 0.00 W
Total Power Allocated (budget) N/A
Total Power Available for additional modules N/A
07-19-2021 06:22 AM
Looking at the bug, still, no resolution, as you mentioned not affecting the working environment, but NMS giving alerts, so suggest to Open a TAC case for an alternative method to fix it.
07-19-2021 06:54 AM
07-19-2021 08:27 AM
sure that is the best option (only you have) since the bug is under investigation.