06-11-2021 12:47 PM
Hi,
I have a customer that has split Nexus devices between DCs and is possibly using vPC between the DCs. I have read this is not recommended and OTV to be used. I was reading this article and also noticed that HSRP when configured on Dual Nexus and vPC actually responds in an active/active fashion.
https://www.ciscozine.com/nexus-vpc-hsrp-vrrp-active-active/
It mentions that the peer device responds for all HSRP macs and then gives it to the Primary. Would this cause issues within L2 environment if the DCs were physically separate with peer in second data centre and the WAN exit back at the primary DC? There would be some delay based on latency between DCs. Is there a threshold or anything above 1ms in the DC is a no no?
Also, if customer has two fibres, between the DC do they transport all vpc traffic over a bundled link or one is dedicate for control traffic? (I haven't seen config yet of these Nexus device)
For context, the design has been as follows -
Outbound from host -----
1. Host in VLAN 100 has default gateway of Nexus HSRP (split across two DCs)
2. Nexus then forwards to a firewall (IN THE SAME VLAN...what the?)
3. Traffic flows over firewall and enters WAN VLAN and is routed to another Nexus HSRP (split across two DCs)
4. Nexus forwards to WAN device (in the SAME VLAN)
Inbound -
1. WAN to Nexus to Firewall
2. Firewall then sends direct to host due to ARP. So traffic is asymmetric.
Thanks
Solved! Go to Solution.
06-14-2021 12:55 AM - edited 06-14-2021 12:56 AM
Most likely a micro burst and buffer exhaustion issue (common issue on FEXs).
Cheers,
Sergiu
06-13-2021 11:31 PM
If you say that your customer has a vpc domain split in two DCs, meaning one vPC peer in one DC and another vPC peer in the second DC, that is definitely something which is not a good idea. First, what is the point of having vPC like that since the whole purpose of vPC is to offer redundancy on layer 2, where the devices are logically one virtual switch. Plus, if there is any fiber cut and peer-link goes down, one DC (where the operational secondary peer is located) will go down. So if you have this, I would suggest you rethink the design of the DCI.
If on the other hand, you are talking about 2 vPC domains back-to-back, with a vPC port-channel between them, then this is something else. This is a supported design. It has some caveats but is supported.
Stay safe,
Sergiu
06-13-2021 11:40 PM
06-14-2021 12:05 AM
Hello,
"I know they have 2 Nexus at one DC and 2 at another with spanned VLANs."
So that most likely means that each pair represents a vPC domain and you have a back-to-back vpc design as DCI:
For this design to work, you need to implement something which is called "HSRP isolation", where you filter the HSPR msgs between the vpc peers (over DCI) to enforce having active VIP in each DC. The config is present in the link above.
Stay safe,
Sergiu
06-14-2021 12:45 AM
Out of the blue, I just heard they moved our WAN router (ASR 1001) from a FEX Fabric Extender via NExus 5k (N2K-C2248TP-1GE) to a new Nexus 9000 switch and the upload issue is resolved.
Previously via iPerf I could not push more than 50 Mbits up and 400mbits down with one tcp stream. I can now do it both ways at 400Mbits.
06-14-2021 12:55 AM - edited 06-14-2021 12:56 AM
Most likely a micro burst and buffer exhaustion issue (common issue on FEXs).
Cheers,
Sergiu