06-29-2020 01:39 AM
Hi all
Is a Breakout cable required to connect Nexus 2348UPQ Fex to a Cisco Nexus 9300 Switch(as Parent)?
A- Can we connect the N2348UPQ to Nexus 9336C-FX2 (36 X 40G) , with the 40G ports on both sides? or Breakout cable is required?
Same question about connecting a Nexus 2348UPQ Fex to the following Nexus 9300 Parent switches:
Cisco Nexus 93180YC-FX 48 x 1/10/25-Gbps fiber ports and 6 x 40/100-Gbps QSFP28 ports
Cisco Nexus 93360YC-FX2 96 x 1/10/25-Gbps fiber ports and 12 x 40/100-Gbps QSFP28 ports
Cisco Nexus 93240YC-FX2 48 x 1/10/25-Gbps fiber ports and 12 x 40/100-Gbps QSFP28 ports
Solved! Go to Solution.
07-02-2020 10:21 PM
Hi S. B,
No you do not need a breakout cable to connect a 2348UPQ to the switches mentioned. A QSFP cable will suffice. Here is what you will need besides the QSFP cable.
Parent Switch | Supported Topologies | Minimum Software Version |
9336C-FX2 | Straight-through | 9.2(1) |
93180YC-FX | Both Straight & Dual-Homed | 9.2(1) |
93360YC-FX2 | Straight-through | 9.3(1) |
93240YC-FX2 | Straight-through |
9.2(1) |
If you find yourself wondering the requirements for other platforms, there is a matrix maintained regarding parent-host and supported fexes found here:
https://www.cisco.com/c/dam/en/us/td/docs/Website/datacenter/fexmatrix/fexmatrix.html
Hth,
Alex
07-02-2020 10:21 PM
Hi S. B,
No you do not need a breakout cable to connect a 2348UPQ to the switches mentioned. A QSFP cable will suffice. Here is what you will need besides the QSFP cable.
Parent Switch | Supported Topologies | Minimum Software Version |
9336C-FX2 | Straight-through | 9.2(1) |
93180YC-FX | Both Straight & Dual-Homed | 9.2(1) |
93360YC-FX2 | Straight-through | 9.3(1) |
93240YC-FX2 | Straight-through |
9.2(1) |
If you find yourself wondering the requirements for other platforms, there is a matrix maintained regarding parent-host and supported fexes found here:
https://www.cisco.com/c/dam/en/us/td/docs/Website/datacenter/fexmatrix/fexmatrix.html
Hth,
Alex
07-03-2020 02:25 PM
Dear @Alex.M
Special Thanks
By the way, I think there is a typo mistake on the link that you sent to me.
Maybe Cisco can Fix It.
when you put the mouse pointer on N9K-C93240YC-FX2 , in NXOS mode, it shows 48x10/25G + 18x40/100G , but on the Cisco nexus 9300 compare web-page(click here), it shows that this switch has 12 x 40/100G uplinks.
Thanks
11-19-2020 04:40 PM
QSFP modules has 2 types of connectors: LC (with multiple channels in different wavelengths) and MPO (with multiple channels in 8 or more fibers - so it's physical).
With the MPO version of QSFP, you can connect A to B with all channels so it's MPO to MPO. A breakout cable can separate a lane from the parallel QSFP interface, then you can create a 1 to N topology to run sub-rate (40G - 4x10G, or 100G - 4x 25G). People configure spine/leaf, and redundancy with this approach.
Happy to share more ...