cancel
Showing results for 
Search instead for 
Did you mean: 
cancel
1484
Views
0
Helpful
3
Replies

Prime Infrastructure 2.1 - Fan-Failure SNMP-Trap Issue

csabarigo
Level 1
Level 1

Hello,

I am facing the following Prime Infrastructure (v2.1) issue:


- A Fan-Failure SNMP-Trap from a Cisco 3650 switch doesn't appear on Prime, but a Link-Failure from the same switch does.
- The both events appears on Prime with Syslog.
- The command "snmp-server enable traps envmon fan shutdown supply temperature status" is set up.
- The switch is in "Managed" state in PI, I have checked the ACL at the "snmp-server community" command, it is okay.
- I have set up an SNMP-Trace for the switch on PI, but only "SNMP Null was returned for class com.cisco.server.managedobjects.bridge.Fan3KStats attribute fanIndex" arrived. Please find the log below.


07/02/14 12:39:53.211 TRACE [presence-9] [] Adding attributes for object Fan3KStats[151206060_,1012]
07/02/14 12:39:53.211 TRACE [presence-9] [] Index name : fanIndex
07/02/14 12:39:53.211 TRACE [presence-9] [] Index Value : 1012
07/02/14 12:39:53.211 TRACE [presence-9] [] Device MIB table index: .1012
07/02/14 12:39:53.211 TRACE [presence-9] [] MIB table row index: .1012
07/02/14 12:39:53.211 TRACE [presence-9] []     OID for : fanIndex = 1.3.6.1.2.1.47.1.1.1.1.1.1012
07/02/14 12:39:53.211 TRACE [presence-9] []     OID for : fanOperStatus = 1.3.6.1.4.1.9.9.13.1.4.1.3.1012
07/02/14 12:39:53.211 TRACE [presence-9] [] Get fragment
07/02/14 12:39:53.211 TRACE [presence-9] [] Creating PDU: Get
07/02/14 12:39:53.211 TRACE [presence-9] []     VarBind OID=1.3.6.1.2.1.47.1.1.1.1.1.1010
07/02/14 12:39:53.211 TRACE [presence-9] []     VarBind OID=1.3.6.1.4.1.9.9.13.1.4.1.3.1010
07/02/14 12:39:53.211 TRACE [presence-9] []     VarBind OID=1.3.6.1.2.1.47.1.1.1.1.1.1011
07/02/14 12:39:53.211 TRACE [presence-9] []     VarBind OID=1.3.6.1.4.1.9.9.13.1.4.1.3.1011
07/02/14 12:39:53.211 TRACE [presence-9] []     VarBind OID=1.3.6.1.2.1.47.1.1.1.1.1.1012
07/02/14 12:39:53.211 TRACE [presence-9] []     VarBind OID=1.3.6.1.4.1.9.9.13.1.4.1.3.1012
07/02/14 12:39:53.218 TRACE [presence-9] [] Error Status: 0
07/02/14 12:39:53.218 TRACE [presence-9] [] Error index:  0
07/02/14 12:39:53.218 TRACE [presence-9] [] SNMP Null was returned for class com.cisco.server.managedobjects.bridge.Fan3KStats attribute fanIndex
07/02/14 12:39:53.218 TRACE [presence-9] []     Setting attribute: fanOperStatus
07/02/14 12:39:53.218 TRACE [presence-9] []     SnmpInt Value : ?
07/02/14 12:39:53.218 TRACE [presence-9] [] GetMultiAttributes, storing result, class=com.cisco.server.managedobjects.bridge.Fan3KStats, attr=fanOperStatus
07/02/14 12:39:53.218 TRACE [presence-9] [] SNMP Null was returned for class com.cisco.server.managedobjects.bridge.Fan3KStats attribute fanIndex
07/02/14 12:39:53.218 TRACE [presence-9] []     Setting attribute: fanOperStatus
07/02/14 12:39:53.218 TRACE [presence-9] []     SnmpInt Value : ?
07/02/14 12:39:53.218 TRACE [presence-9] [] GetMultiAttributes, storing result, class=com.cisco.server.managedobjects.bridge.Fan3KStats, attr=fanOperStatus
07/02/14 12:39:53.218 TRACE [presence-9] [] SNMP Null was returned for class com.cisco.server.managedobjects.bridge.Fan3KStats attribute fanIndex
07/02/14 12:39:53.218 TRACE [presence-9] []     Setting attribute: fanOperStatus
07/02/14 12:39:53.218 TRACE [presence-9] []     SnmpInt Value : ?
07/02/14 12:39:53.218 TRACE [presence-9] [] GetMultiAttributes, storing result, class=com.cisco.server.managedobjects.bridge.Fan3KStats, attr=fanOperStatus
07/02/14 12:39:53.218 TRACE [presence-9] [] GetMultiAttributes, assembling attributes
07/02/14 12:39:53.218 TRACE [presence-9] []     MIB lookup, OID for: powerSupplyIndex = 1.3.6.1.2.1.47.1.1.1.1.1
07/02/14 12:39:53.218 TRACE [presence-9] []     GetMultiAttributes needs class=com.cisco.server.managedobjects.bridge.PowerSupply3kStats, field=powerSupplyIndex
07/02/14 12:39:53.218 TRACE [presence-9] []     MIB lookup, OID for: powerSupplyOperStatus = 1.3.6.1.4.1.9.9.13.1.5.1.3
07/02/14 12:39:53.218 TRACE [presence-9] []     GetMultiAttributes needs class=com.cisco.server.managedobjects.bridge.PowerSupply3kStats, field=powerSupplyOperStatus
07/02/14 12:39:53.218 TRACE [presence-9] [] GetMultiAttributes invoked
07/02/14 12:39:53.218 TRACE [presence-9] [] GetMultiAttributes building OIDs for next PDU
07/02/14 12:39:53.218 TRACE [presence-9] [] Adding attributes for object PowerSupply3kStats[151206060_,1009]


- The switch sends the SNMP Trap, based on the followings:


Jul  7 13:38:30 UTC: SNMP: Packet sent via UDP to IP_ADDRESS
Jul  7 13:38:30 UTC: %PLATFORM_THERMAL-6-FRU_FAN_OIR: Switch 1: System fan 1 removed
Jul  7 13:38:30 UTC: %PLATFORM_THERMAL-1-FRU_FAN_NOT_PRESENT: Switch 1: System fan 1 not present
Jul  7 13:38:30 UTC: SNMP: Queuing packet to IP_ADDRESS
Jul  7 13:38:30 UTC: SNMP: V2 Trap, reqid 33202, errstat 0, erridx 0
sysUpTime.0 = 576753333
snmpTrapOID.0 = ciscoEnvMonMIBNotifications.8
ciscoEnvMonFanStatusEntry.2.1010 = Switch 1 - FAN 1, NotExist
ciscoEnvMonFanStatusEntry.3.1010 = 5
Jul  7 13:38:30 UTC: SNMP: Queuing packet to IP_ADDRESS
Jul  7 13:38:30 UTC: SNMP: V2 Trap, reqid 33203, errstat 0, erridx 0
sysUpTime.0 = 576753333
snmpTrapOID.0 = ciscoEnvMonMIBNotifications.8
ciscoEnvMonFanStatusEntry.2.1010 = Switch 1 - FAN 1, NotExist
ciscoEnvMonFanStatusEntry.3.1010 = 5
Jul  7 13:38:30 UTC: SNMP: Queuing packet to IP_ADDRESS
Jul  7 13:38:30 UTC: SNMP: V2 Trap, reqid 33204, errstat 0, erridx 0
sysUpTime.0 = 576753333
snmpTrapOID.0 = ciscoEnvMonMIBNotifications.8
ciscoEnvMonFanStatusEntry.2.1010 = Switch 1 - FAN 1, NotExist
ciscoEnvMonFanStatusEntry.3.1010 = 5
Jul  7 13:38:30 UTC: SNMP: Queuing packet to IP_ADDRESS
Jul  7 13:38:30 UTC: SNMP: V2 Trap, reqid 33205, errstat 0, erridx 0
sysUpTime.0 = 576753333
snmpTrapOID.0 = ciscoEnvMonMIBNotifications.8
ciscoEnvMonFanStatusEntry.2.1010 = Switch 1 - FAN 1, NotExist
ciscoEnvMonFanStatusEntry.3.1010 = 5
Jul  7 13:38:31 UTC: SNMP: Packet sent via UDP to IP_ADDRESS
Jul  7 13:38:31 UTC: SNMP: Packet sent via UDP to IP_ADDRESS
Jul  7 13:38:31 UTC: SNMP: Packet sent via UDP to IP_ADDRESS
Jul  7 13:38:31 UTC: SNMP: Packet sent via UDP to IP_ADDRESS 
Jul  7 13:38:45 UTC: SNMP: Packet sent via UDP to IP_ADDRESS
Jul  7 13:38:51 UTC: %PLATFORM_THERMAL-6-FRU_FAN_OIR: Switch 1: System fan 1 inserted
Jul  7 13:38:54 UTC: SNMP: Queuing packet to IP_ADDRESS
Jul  7 13:38:54 UTC: SNMP: V2 Trap, reqid 33206, errstat 0, erridx 0
sysUpTime.0 = 576755733
snmpTrapOID.0 = ciscoEnvMonMIBNotifications.8
ciscoEnvMonFanStatusEntry.2.1010 = Switch 1 - FAN 1, Normal
ciscoEnvMonFanStatusEntry.3.1010 = 1
Jul  7 13:38:54 UTC: SNMP: Queuing packet to IP_ADDRESS
Jul  7 13:38:54 UTC: SNMP: V2 Trap, reqid 33207, errstat 0, erridx 0
sysUpTime.0 = 576755733
snmpTrapOID.0 = ciscoEnvMonMIBNotifications.8
ciscoEnvMonFanStatusEntry.2.1010 = Switch 1 - FAN 1, Normal
ciscoEnvMonFanStatusEntry.3.1010 = 1
Jul  7 13:38:54 UTC: SNMP: Queuing packet to IP_ADDRESS
Jul  7 13:38:54 UTC: SNMP: V2 Trap, reqid 33208, errstat 0, erridx 0
sysUpTime.0 = 576755733
snmpTrapOID.0 = ciscoEnvMonMIBNotifications.8
ciscoEnvMonFanStatusEntry.2.1010 = Switch 1 - FAN 1, Normal
ciscoEnvMonFanStatusEntry.3.1010 = 1
Jul  7 13:38:54 UTC: SNMP: Queuing packet to IP_ADDRESS
Jul  7 13:38:54 UTC: SNMP: V2 Trap, reqid 33209, errstat 0, erridx 0
sysUpTime.0 = 576755733
snmpTrapOID.0 = ciscoEnvMonMIBNotifications.8
ciscoEnvMonFanStatusEntry.2.1010 = Switch 1 - FAN 1, Normal
ciscoEnvMonFanStatusEntry.3.1010 = 1
Jul  7 13:38:55 UTC: SNMP: Packet sent via UDP to IP_ADDRESS
Jul  7 13:38:55 UTC: SNMP: Packet sent via UDP to IP_ADDRESS
Jul  7 13:38:55 UTC: SNMP: Packet sent via UDP to IP_ADDRESS
Jul  7 13:38:55 UTC: SNMP: Packet sent via UDP to IP_ADDRESS


It seems like PI and the switch doesn't understand each other concerning the fan...

Thanks for any ideas, comments and feedbacks,

Csaba

3 Replies 3

fodorcs
Level 1
Level 1

I have the very same problem.

The switch has a power supply error (one of the two is down). There is the syslog message in PI about it, but no event has created, so nor alarm is there as well.

When I check the status of the switch in the Device Work Center, and choose the Environment in Device Details I can see that PI has not realized the power supply error.

However when I click on the Sync for this very device the power supply status is updated, but still no event or alarm.

This is the case with the FANs as well.

hi,

had the same issue, please check:

https://tools.cisco.com/bugsearch/bug/CSCug91416

 

Greetings

Falk

 

Hi Falk,

 

Thank you, yes we are facing the same problem. So we have to wait for the patch.

 

Kind Regards,

Csaba

 

Getting Started

Find answers to your questions by entering keywords or phrases in the Search bar above. New here? Use these resources to familiarize yourself with the community: