02-06-2013 09:36 AM - edited 03-01-2019 07:15 AM
When reading
I have a few questions about "Figure 6-1 Enhanced vPC Topology" when upgrading the N5K with the DH FEX Configuration.
1. Is there any actual downtime for the host at the bottom ?
2. When upgrading the Nexus 5K, at which point will which FEX reload ?
All the help is appreciated ;-)
02-06-2013 02:21 PM
Errrr ... This kind of design is not recommended.
It is recommended that your FEX be homed to ONE Nexus 7K/5K. You can have multiple uplinks to a single Nexus 7K/5K.
02-06-2013 11:12 PM
The question is about first, supported configuration.....
Sent from Cisco Technical Support iPhone App
02-06-2013 11:12 PM
Hi,
1. There should not be any downtime for the host.
2. If its non-disrputive ISSU (rolling upgrade) the FEX is not going to reboot.
Thanks
JayaKrishna
02-07-2013 04:29 AM
Ok but at what time will the FEX reboot. The OS will be different between FEX and N5K...
Sent from Cisco Technical Support iPhone App
02-07-2013 08:42 PM
The FEX does not reload , it will be upgraded without a reload. Please look at the following link:
Cisco NX-OS supports in-service software upgrades (ISSUs) that allow a Cisco Nexus device and any connected FEXs to be upgraded without any traffic disruption (with a brief control plane disruption). A few conditions have to be met for the system to be upgraded via ISSU process - the access layer topology should be ISSU compliant, the current and target versions should be ISSU capable and the network should be stable.
If the conditions required for ISSU are not met or if the user intends to downgrade the software version, the installation process is disruptive. For example the Cisco Nexus device and any connected FEX are rebooted, which causes a disruption. If Cisco's virtual port channel (vPC) is configured on Cisco Nexus devices, it is possible to achieve an upgrade/downgrade with very minimal traffic disruption to servers/hosts.
With a single supervisor system like a Cisco Nexus device, an ISSU on the Cisco Nexus device causes the supervisor CPU to reset and load the new software version. The control plane is inactive, but the data plane keeps forwarding packets that lead to an upgrade with no service disruption. After the CPU loads the updated version of Cisco NX-OS, the system restores the control plane to a previously known configuration and the runtime state and the data plane are synchronized. Because the data plane keeps forwarding packets while the control plane is upgraded, any servers connected to the Cisco Nexus device access layer should see no traffic disruption.
Cisco Nexus Fabric Extenders act as line cards to Cisco Nexus devices. The fabric extenders add flexibility to datacenter networking infrastructure by decoupling the physical and logical (Layer 2) topology, reducing the operation expense by lowering management and troubleshooting points, and building a larger layer 2 fabric that is loop-free, with a single layer of switching.
The ISSU process initiated on the Cisco Nexus devices upgrades the entire access layer including the switch and the FEXs that are connected to the switch.
An ISSU first upgrades the switches. Once the switch is operational with the upgraded software, the FEX's are upgraded. This upgrade of the FEX is done in a rolling fashion, one FEX at a time. This upgrade on the Cisco Nexus Fabric Extenders is non-disruptive, similar to the upgrade of the switch.
The time required for an ISSU to complete depends on the number of FEX's that are connected. You should plan a maintenance window with the total upgrade time in mind. The entire upgrade is non-disruptive and is not expected to cause any outage to connected servers.
Hope this helps.
JayaKrishna
09-02-2013 07:00 AM
Hello
According to the Cisco site, the upgrade of a Dual-Homed FEX Access Layer is disruptive to the hosts connected to a single FEX & needs a special procedure reloading the FEX manually :
it seems disapoiting, as Enhanced vPC is supposed to add redundancy but it makes ISSU disruptive... while it is not when not using Enhanced vPC (figure 16 above is said non disruptive)