10-20-2016 02:06 AM
For our new datacenter network I have 4 Nexus 5672UP's in two datacenters. Between the datacenters is a redundant vPc with 2x10Gb fibers. I've configured two VPC domains, one for each datacenter. I have read that HSRP within a VPC domain is active/active, however I wonder what would be the proper way to configure the HSRP setup for the stretched VLAN's since they are in two different vPc domains?
Solved! Go to Solution.
10-20-2016 02:55 AM
If you need FHRP isolation between the sites, this can be achieved by configuring HSRP authentication at one site therefore stopping the HSRP hellos between the sites from being processed and allowing each site to act in Active/Standby state. Due to the HW architecture on the Nexus 5600, control plane multicast packets are punted to the CPU ignoring any PACL or MAC-ACL. So with a PACL, you will not be able to filter HSRP Hellos, ARP, BPDUs, etc. which need to go to the CPU, because there is a pre-defined ACL to redirect control traffic to CPU and this ACL that takes precedence over the user-configured ACL. It is recommended to configure "no ip arp gratuitous hsrp duplicate" to suppress the un-necessary GARPs at each site in this design as well. Also note 4-way HSRP is only supported on the latest NX-OS versions, refer to CSCuy89705.
Another solution is to run FabricPath DCI with Anycast HSRP which will allow all 5600s to act as an active default gateway, refer to page 22 of the Cisco FabricPath Best Practices.
- Tyler Jeffords
10-20-2016 02:55 AM
- Tyler Jeffords