Hi Sirs. 

                

I have a catalyst WS-4510R+E, with 2 x SUP 7E, and 2 modules WS-X4748-RJ45V+E, and IOS cat4500e-universalk9.SPA.03.02.00.SG.150-2.SG.bin.

Now i need install one AIR-LAP1231G-A-K9 with power supply the module PoE off catalyst.

But when i connect the cable, the catalyst generate the following log:

%PM-4-ERR_DISABLE: inline-power error detected on Gi1/31, putting Gi1/31 in err-disable state

%ILPOWER-5-ILPOWER_POWER_DENY: Interface Gi1/31: inline power denied. Reason: Insufficiente inlie power, requested(31579) available(0).

4510-R#show power inline g1/31
Available:0(w)  Used:0(w)  Remaining:0(w)

Interface Admin  Oper            Power(Watts)     Device              Class
                            From PS    To Device                   
--------- ------ ---------- ---------- ---------- ------------------- -----

Gi1/31    auto   off        0.0        0.0        n/a                 n/a 

Interface  AdminPowerMax   AdminConsumption   
             (Watts)           (Watts)          
---------- --------------- -------------------- 

Gi1/31                30.0                 15.4

could anyone give any tips?

is missing any setting?

1 Accepted Solution

Accepted Solutions

amikat
Spotlight
Spotlight

Hi,

I am sorry to let you know that your PSU type PWR-C45-1400AC does NOT support PoE (ie. it is for data only), please see eg. the document beneath:

http://www.cisco.com/en/US/prod/collateral/switches/ps5718/ps4324/product_data_sheet0900aecd801792b1.html

PSUs to support both Data and PoE are listed in the table 8 down the document (while you PSU is listed in the table 7).

Best regards,

Antonin

View solution in original post

6 Replies 6

Arumugam Muthaiah
Cisco Employee
Cisco Employee

Hi Cedrick,

This error message indicates that there is insufficiant inline power, could you please share the #show power detail output to check this issue further.

Regards,

Aru

*** Please rate if the post is useful ***

Regards, Aru *** Please rate if the post useful ***

Hi Arumugam.

Following the output:

4510-R#show power detail
Power                                             Fan      Inline
Supply  Model No          Type       Status       Sensor   Status
------  ----------------  ---------  -----------  -------  -------
PS1     PWR-C45-1400AC    AC 1400W   good         good     n.a.  
PS2     none              --         --           --       --    

Power supplies needed by system    : 1
Power supplies currently available : 1

Power Summary                      Maximum
(in Watts)              Used     Available
----------------------   ----     ---------
System Power (12V)       1108        1360
Inline Power (-50V)         0           0
Backplane Power (3.3V)     40          40
----------------------   ----     ---------
Total                    1148        1400


                             Watts Used of System Power(12V)
Mod   Model                 budgeted instantaneous  peak   out of reset  in reset
----  -------------------   -------- ------------- ------  ------------  --------
1    WS-X4748-RJ45V+E          75          51        51        75          35
2    WS-X4748-RJ45V+E          75          40        41        75          35
5    WS-X45-SUP7-E            260         199       208       260         100
6    WS-X45-SUP7-E            225         191       196       225         225
7    WS-X4612-SFP-E            40         --        --         40           5
9    WS-X4648-RJ45-E           89         --        --         89          10
10    WS-X4648-RJ45-E           89         --        --         89          10
--   Fan Tray                 255         --        --        --          --
-------------------------   -------- ------------- ------  ------------  --------
       Total                  1108         481       496       853         420

                        Watts used of Chassis Inline Power (-50V)
                        Inline Power Admin  Inline Power Oper
Mod   Model                PS     Device       PS     Device     Efficiency
----  -------------------  ----------------    ----------------    ----------
1    WS-X4748-RJ45V+E         -        -          -        -           -
2    WS-X4748-RJ45V+E         -        -          -        -           -
5    WS-X45-SUP7-E            -        -          -        -           -
6    WS-X45-SUP7-E            -        -          -        -           -
7    WS-X4612-SFP-E           -        -          -        -           -
9    WS-X4648-RJ45-E          -        -          -        -           -
10    WS-X4648-RJ45-E          -        -          -        -           -
-------------------------  ----------------    ----------------    ----------
       Total                   0        0          0        0
         

apparently everything is right.

I would say you might have insufficient power supplies for what you  have, 1400W is not much . One way to test would be during a window change the power supplies from redundant to combined and see if that fixes it .  If the chassis doesnt have enough power the card may be active but it wont supply inline power. I just noticed you only have a single supply so what I reccomended above wont work. You may need a 4000W supply .

Agree with Glen.  You have a single 1400W power supply and you have TWO PoE blades.

You need to upgrade your PS with a 4kW unit (and this does not factor in PS redundancy).

amikat
Spotlight
Spotlight

Hi,

I am sorry to let you know that your PSU type PWR-C45-1400AC does NOT support PoE (ie. it is for data only), please see eg. the document beneath:

http://www.cisco.com/en/US/prod/collateral/switches/ps5718/ps4324/product_data_sheet0900aecd801792b1.html

PSUs to support both Data and PoE are listed in the table 8 down the document (while you PSU is listed in the table 7).

Best regards,

Antonin

Thank´s sirs.

I will evaluate the cost of a new PSU with support PoE.