Does any know the command to determine if the PS are in combined or redundant mode on both the 65xx and 45xx chasis?
Thanks in advance.
On the 6500, the command "sh power" will tell you right away.
system power redundancy mode = redundant
system power total = 2671.20 Watts (63.60 Amps @ 42V)
system power used = 1463.70 Watts (34.85 Amps @ 42V)
system power available = 1207.50 Watts (28.75 Amps @ 42V)
Power-Capacity PS-Fan Output Oper
PS Type Watts A @42V Status Status State
1 WS-CAC-6000W 2671.20 63.60 OK OK on
2 WS-CAC-6000W 2671.20 63.60 OK OK on
Pwr-Allocated Oper
Fan Type Watts A @42V State
1 WS-C6509-E-FAN 210.00 5.00 OK
Pwr-Requested Pwr-Allocated Admin Oper
Slot Card-Type Watts A @42V Watts A @42V State State
1 WS-X6716-10GE 457.80 10.90 457.80 10.90 on on
5 VS-S720-10G 338.10 8.05 338.10 8.05 on on
6 WS-X6716-10GE 457.80 10.90 457.80 10.90 on on
system auxiliary power mode = off
system auxiliary power redundancy operationally = non-redundant
system primary connector power limit = 10920.00 Watts (260.00 Amps @ 42V)
system auxiliary connector power limit = 10500.00 Watts (250.00 Amps @ 42V)
system primary power used = 1463.70 Watts (34.85 Amps @ 42V)
system auxiliary power used = 0 Watt
On the cat 4500, you have to use some déduction...I have two 4200w power supply and I have 8400w available...
Power Fan Inline
Supply Model No Type Status Sensor Status
PS1 PWR-C45-4200ACV AC 4200W good good good
PS1-1 220V good
PS1-2 220V good
PS2 PWR-C45-4200ACV AC 4200W good good good
PS2-1 220V good
PS2-2 220V good
Power supplies needed by system : 2
Power supplies currently available : 2
Power Summary Maximum
(in Watts) Used Available
System Power (12V) 716 2200
Inline Power (-50V) 968 6200
Backplane Power (3.3V) 0 40
Total 1684 (not to exceed Total Maximum Available = 7600)
Power Measurement Inline Power (-50V)
(in Watts) (+/- 50Watts)
PS1 350
PS2 150
Total 500
The best way is to do a show run and look the power redundancy-mode combined command. If it's not there, its the default of redundant.