Catalyst 9300 temp monitoring.

Greetings,

 

I was looking at getting the 9300 temp sensors into our monitoring system, but am unsure as to what the values actually are.

Below is an example. I know it's not Celsius as it's in a temp controlled room and it's not 80 degrees in there, and it's not Fahrenheit as it's not that cold either.

 

Is there a conversion or anything on the values?

 

ciscoEnvMonTemperatureStatusDescr.1012Switch 1 - Inlet Temp Sensor, GREENOctetString10.10.2.52:161
ciscoEnvMonTemperatureStatusDescr.1013Switch 1 - Outlet Temp Sensor, GREENOctetString

10.10.2.52:161

ciscoEnvMonTemperatureStatusValue.101227Gauge10.10.2.52:161
ciscoEnvMonTemperatureStatusValue.101330Gauge10.10.2.52:161
ciscoEnvMonTemperatureThreshold.101256Integer10.10.2.52:161
ciscoEnvMonTemperatureThreshold.1013125Integer10.10.2.52:161
1 Reply 1

JohnBaird
Level 1
Level 1

Did you find an answer? Looking at the above I see the temperature of the air flowing in is 27°c and the air flowing out is 30°c, which seem like reasonable values - but do they line up with the actual room temperature? The alarm values of 57°c on the incoming air and 125°c on the outgoing air seem a little high, but I guess it's all solid-state stuff and if they are shutdown temperatures could be acceptable for a short burst.