Power should provided for Nexus 7010 in my Rack
lcd_shouldit
Hi, there are 3 7.5Kw power supply in my Nexus 7010.
and the redundant mode is REDUNDANT.
So what is the exactly power should I provide for this Nexus in my rack.
7.5 x 3 = 22.5 Kw ?
Thanks a lot!
Reza Sharifi
That is correct. 22.5 is the max based on how many blades and sups you have in the chassis.  Each power supply comes with 2 outputs.  For load sharing, it is good idea if you can connect each output to a different PDU. You need c19/c20 power cords to connect the PSUs to the PDUs.
I need to correct Reza here. With current mode of redundancy you will get 11,250W:
Redundant mode means
redundant
Input Source (GRID) + Power Supply Redundancy - The available power is the lesser of the available power for the power supply mode and input source voltage. The difference (50%) is reserved for backup.
http://www.cisco.com/en/US/docs/switches/datacenter/sw/best_practices/cli_mgmt_guide/init_config.html#wp1053349
As per table 5  in the link below 3 PS will give 11.250 in this mode:
http://www.cisco.com/en/US/prod/collateral/switches/ps9441/ps9402/ps9512/Data_Sheet_C78-437761_ps9402_Products_Data_Sheet.html
Niko
HTH,
Niko
Hi, thanks so much!
So, 3 PS will give me 11,250 W in this mode, which is the output.
How about the input, Should I prepare 7.5 x 3 = 22.5Kw for this Nexus ?