You'll need to upgrade the chassis before installing the F2s. And you�ll need to upgrade
both the system and kickstart images.
(http://www.cisco.com/c/en/us/products/collateral/switches/nexus-7000-series-switches/data_sheet_c78-719524.html
AS you can see the these modules only supported from release 6.1.2 or later)
2.
Since you are running a single SUP chassis you�ll need to follow the traditional upgrade
procedure, which can be found here:
http://www.cisco.com/en/US/docs/switches/datacenter/sw/5_x/nx-os/upgrade/guide/b_Cisco_Nex
us_7000_Series_NX-OS_Software_Upgrade_and_Downgrade_Guide__Release_5.x_chapter_00.html#con
_314241
3.
Once the chassis is upgraded you�ll need to create a special VDC for the F2 modules. F2
modules require an isolated VDC. Here are the instructions for creating it:
a.
config t
b.
vdc <name>
c.
limit-resource module-type f2
d.
allocate interface Ethernet <port range>
e.
exit
f.
switchto vdc <name>
4.
The F2s will not inherit the config from the old F1/M1 modules, so you�ll need to
configure them once their installed.
5.
You should be fine from a licensing standpoint, unless you want to do FCoE.
6.
You may also want to take a look at the following flow chart to verify that you have
enough memory to perform he upgrade:
http://www.cisco.com/en/US/docs/switches/datacenter/hw/nexus7000/installation/guide/n7k_re
placing.html#wp1271902
HTH