What is the recommended level of light intensity in a TelePresence room?
01-09-2013 12:51 AM
Hello Kelvin,
Did you check the Telepresence Room Recommendations doc. on CCO :
For a CTS 1100 :
http://www.cisco.com/en/US/docs/telepresence/cts_1100/cts_1100_assembly_guide/1100_room_recommendations.html#wp1154652
For the CTS 1310 :
http://www.cisco.com/en/US/docs/telepresence/cts_1300/cts_1310/assembly/guide/1310_room_recommendations.html#wp1136863
Illumination
Target Measurement in Lux (= lm/m2)
Tolerance
Notes
Overall illumination
300-400 lux
50 lux
All lighting should be evenly dispersed. There should not be areas of 250 and 450 lux in the same room.
Measured vertically with the light sensor pointed at wall or intended camera location (not pointed at the ceiling).
Shoulder light/Direct down light
600-700 lux
Generally, shoulder lighting should not be more the 400 lux greater than the overall illumination of the room, and should never exceed 800 lux
Measured horizontally at table height, with the light sensor pointed at the ceiling
For which TP device do you want the info for ?
/Hans