Hello all,I have a fully populated 5108 chassis with 8 x B200 M5 servers.The chassis has 4 power supplies which are configured in a grid mode.Power supply 1+2 are connected to the same PDU and power supply 3+4are connected to a different PDU.What wil...
Hello all,Is it possible to run a C220 M5 server with one power supply plugged into 220V and the other power supply plugged into 110V at the same time?Appreciate any response,Ron
Each PSU is capable of handling 2500W. 4 x 2500W = 10000W.If 2 PSU's will fail (that means that one PDU is down), the chassiswill have half of its power which means 5000W.I have calculated the amount of power required for the 8 x B200servers on the C...
Thank you for the link however the article only says what kind of Voltage you can use with you power supply, it does not say if mixing a 220V and a 110V is supported. 770W & 1050W AC Input Voltage - Nominal range: 100–120 VAC, 200–240 VAC1600W AC In...
One PDU is conncetd to a 220V electric network and the other PDU is connected to a 110V electric network. This is a live environment and I need to make sure that this kind of configuration is supported.