The documentation for the 3200w power supplies for the 9410 Chassis, I believe, have an error in them.
The documentation erroneously states:
kVA rating11 | 3200W (total output power ) or 3478.3 kVA (high-line operation). |
To calculate kVA the formula is Volts*Amps/1000. For this power supply the equation is (200V AC * 17.6A / 1000)
Making, what I think the correct kVA to be 3.52kVA
The posted kVA of 3478.3. seems to be 1000 times larger than the calculated power consumption of this power supply.
But I am having trouble identifying where is the best place to identify, and confirm, this error.