nexus 9508 power Redundancy Mode help

limyh
Level 1
Level 1

Hi everyone,
I have a question about nexus 9805 power redundancy.
It uses 3000w AC power and is connected to power supply slots 1, 2, 3, and 4.After testing the equipment, I found that the module worked properly when three power sources were connected.
It is confirmed that power is insufficient because the power supply redundancy mode is PS-Redundant.
I want to have redundancy with 4 power sources even if 2 power supplies go out.
So the way I thought about it was


1. Change power supply combine mode
2. Move the power supply to number 3 4 power supply 5 6
3. So, even if power supplies 1 and 2 on one side go out, are all modules normal when you run show module?

1 응답 1

Translator
Community Manager
Community Manager

전원 이중화 설계는 고객이 원하는 것과는 다릅니다
Cisco Nexus 9000 Series NX-OS High Availability and Redundancy Guide, Release 6.x - System-Level High Availability [Cisco Nexus 9000 Series Switches] - Cisco를 참조하십시오.

표 1. 전원 이중화 모드

이중화 모드

설명

결합(비중복)

이 모드는 전원 이중화를 제공하지 않습니다. 가용 전력은 모든 전원 공급 장치의 총 전력 용량입니다.

insrc-redundant(그리드 리던던시)

이 모드는 전원 공급 장치의 절반을 한 그리드에 연결하고 전원 공급 장치의 나머지 절반을 두 번째 그리드에 연결할 때 그리드 이중화를 제공합니다. 사용 가능한 전력은 그리드를 통해 사용 가능한 전력의 양입니다.

그리드 이중화를 활성화하려면 올바른 전력 그리드 슬롯에 전원 공급 장치를 연결해야 합니다. 예를 들어, Cisco Nexus 9508 스위치에서 슬롯 1, 2, 3, 4는 그리드 A에 있고 슬롯 5, 6, 7, 8은 그리드 B에 있습니다. 그리드 이중화 모드에서 구성 및 작동하려면 전원 공급 장치의 절반을 그리드 A의 슬롯에 연결하고 나머지 전원 공급 장치를 그리드 B의 슬롯에 연결해야 합니다. 사용 중인 전원 공급 장치의 전원 그리드 슬롯 할당에 대한 자세한 내용은 사용 중인 특정 Cisco Nexus 9000 Series 플랫폼의 하드웨어 설치 가이드를 참조하십시오.

ps-redundant(N+1 이중화)

이 모드는 활성 전원 공급 장치가 중단될 경우 추가 전원 공급 장치를 제공합니다. 사용 가능한 모든 전원 공급 장치 중 하나의 전원 공급 장치는 추가 전원 공급 장치로 간주되며, 총 가용 전원은 활성 전원 공급 장치에서 제공하는 양입니다.