07-24-2013 10:00 PM - edited 03-01-2019 07:22 AM
I am getting the following error on N7K
%PLATFORM-1-PFM_ALERT: POWER_OVER_BUDGET: Power has dropped. Existing power is insufficient
What does it mean?
07-24-2013 11:46 PM
As a starting point enter all the blades you have installed in your switch into the power calculator below:
The power supply you have installed in the switch may not have sufficient capacity to support the number and types of blades installed.
Don't forget to rate all helpful posts.
07-25-2013 12:30 AM
Hi ,
The strange thing is that we have another N7k which has more blades than this N7k and it is not showing any alerts !!!!
This is the output of my environment power details
NDOHHQSWI700901# show environment power de
Power Supply:
Voltage: 50 Volts
Power Actual Total
Supply Model Output Capacity Status
(Watts ) (Watts )
1 N7K-AC-6.0KW 0 W 0 W Ok
2 N7K-AC-6.0KW 1795 W 3000 W Ok
Actual Power
Module Model Draw Allocated Status
(Watts ) (Watts )
1 N7K-SUP2 107 W 190 W Powered-Up
2 N7K-SUP2 105 W 190 W Powered-Up
3 N7K-M224XP-23L 680 W 795 W Powered-Up
4 N7K-M148GT-11L 313 W 400 W Powered-Up
5 N7K-M148GT-11L 287 W 400 W Powered-Up
Xb1 N7K-C7009-FAB-2 N/A 70 W Powered-Up
Xb2 N7K-C7009-FAB-2 N/A 70 W Powered-Up
Xb3 N7K-C7009-FAB-2 N/A 70 W Powered-Up
Xb4 N7K-C7009-FAB-2 N/A 70 W Powered-Up
Xb5 N7K-C7009-FAB-2 N/A 70 W Powered-Up
fan1 N7K-C7009-FAN 92 W 650 W Powered-Up
N/A - Per module power not available
Power Usage Summary:
Power Supply redundancy mode (configured) PS-Redundant
Power Supply redundancy mode (operational) Non-Redundant
Total Power Capacity (based on configured mode) 3000 W
Total Power of all Inputs (cumulative) 3000 W
Total Power Output (actual draw) 1795 W
Total Power Allocated (budget) 3125 W
Total Power Available for additional modules 0 W
Power Usage details:
Power reserved for Supervisor(s): 530 W
Power reserved for Fabric Module(s): 350 W
Power reserved for Fan Module(s): 650 W
Total power reserved for Sups,Fabrics,Fans: 1530 W
Are all inlet chords connected: No
Power supply details:
PS_1 total capacity: 0 W Voltage:50V
chord 1 capacity: 0 W
chord 1 not connected
chord 2 capacity: 0 W
chord 2 not connected
Software-Alarm: No
Hardware alarm_bits reg0:4E, reg3:10, reg4:FF, reg5:FF, reg6:FF, reg7:FF,
Reg0 bit1: restarted successfully
Reg0 bit2: shutdown had occured (in the past)
Reg0 bit3: loss of line1
Reg0 bit6: Invalid access
Reg3 bit4: reserved
PS_2 total capacity: 3000 W Voltage:50V
chord 2 capacity: 3000 W
chord 2 connected to 220v AC
Software-Alarm: No
Hardware alarm_bits reg0: 2, reg4:FF, reg5:FF, reg6:FF, reg7:FF,