I am in need of the heat output of the 4431 router NON-PoE and am not able to find this in the product data sheet.
Understand the environment specs but need to device BTU output for HVAC planning in the data center,
Thanks
Scott
07-07-2017 10:29 AM
Hello,
this is all I can find:
Power consumption
60 to 250 W (205 to 853 BTU/hr) (configuration dependent)
07-07-2017 11:24 AM
Thank You
Power was an easy find and I will take the BTU details forward for planning purposes
Scott
03-18-2019 09:51 AM
I'm just wondering if we can use maximum power draw for HVAC load calc purpose. Per ASHRAE, "A power supply nameplate rating indicates the maximum power draw for the datacom equipment’s safety and regulatory approval. A nameplate rating does not represent actual power draw during usage and should not be used as a measurement of datacom equipment heat release."
Please advise.