Dear All,
Can anyone help to understand why getting temperature event in 3560 switch, and we checked the Network room Temp it's normal around (22).
What could be the cause for this?
Any update will highly appreciated
Regards,
Prasad
Solved! Go to Solution.
03-14-2013 10:38 AM
Hi Prasad
I think you will need to increase the threshold, I just checked the datasheet for these switches, its operation temperature range 0-45C. Per design, you will be alarmed when its temp reaches the yellow threshold and it will power down to protect itself when it reaches to the red threshold. form thow enviroment all, here are the threshold of your switch:
Yellow Threshold : 46 Degree Celsius
Red Threshold : 60 Degree Celsius
and here is the link for the datasheet
Regards
03-10-2013 09:34 PM
Sometimes similar issues could be caused either by blocked airflow or bad sensor, check if there are other devices closed to this one and make sure the temp is within acceptable ranges
Sent from Cisco Technical Support iPhone App
03-11-2013 03:48 AM
Dear Amjad,
Thanks for your update, we have check the physically to device, there is no issue with airflow both power supply is working properly. Can you let me know how can I check the sensor status of the device? and surrounding to that all the devices is having normal temperature only two device 3560 is having temp issue.
Kindly suggest the possible solution.
Thanks
03-11-2013 10:48 AM
Can you provide the show enviroment all
usually the only way to find out if the sensor status other than check the measured temp, if it is not providing correct readings then that means it is not working properly. If you can clean the dust on these switches, use a blower and check after than, I dont expect the sensors on these two switches stop working at the same time.
03-13-2013 03:17 AM
Thanks Amhad for prompt reply.
Will check the suggested things plz find attached below log for bith switches.
**********************************************************************************************
SW1#sh env all
**********************************************************************************************
03-13-2013 12:15 PM
the logs is not showing any issues,
TEMPERATURE is OK
Temperature Value: 31 Degree Celsius
where do you see the temp alarms? via snmp or it is in show log?
03-14-2013 03:43 AM
Dear Amjad,
Temperature issue is not coming continuously it’s fluctuating. And temp error message is generating through the SNMP monitoring tool. And we have configured threshold value in system 35C.
Can you let us know the max limit Tamp of Cisco devices?
Regards,
Prasad
03-14-2013 10:38 AM
Hi Prasad
I think you will need to increase the threshold, I just checked the datasheet for these switches, its operation temperature range 0-45C. Per design, you will be alarmed when its temp reaches the yellow threshold and it will power down to protect itself when it reaches to the red threshold. form thow enviroment all, here are the threshold of your switch:
Yellow Threshold : 46 Degree Celsius
Red Threshold : 60 Degree Celsius
and here is the link for the datasheet
Regards
03-15-2013 05:03 AM
Thanks Bhai for your update....