cancel
Showing results forĀ 
Search instead forĀ 
Did you mean:Ā 
cancel
869
Views
0
Helpful
1
Replies

9700 power alarm

Hi gents, I have a strange issue on on  9718; we installed many 9700 in a datacenter, do redundancy power and supervisor checks, all was fine, ready to migrate... It happends one day all the power supplies on one switch were in alarm. I powered off the 12 power supplies, then on, and it was OK... but happened again this morning. AC input has been checked, there are 6 separate input lines. I couldn't find any troubleshooting guide. We will replace the chassis and perhaps get the tech-support...

Just for information, firmware is  7.3(0)D1(1)

1 Reply 1

Rick1776
Level 5
Level 5
How is the power configured as:
Combined mode
Power supply redundancy mode (N+1)
Input grid redundancy mode (grid redundancy)
Full redundancy mode

Please see the following link for the configuration....

https://www.cisco.com/c/en/us/td/docs/switches/datacenter/mds9000/sw/8_x/config/fundamentals/cisco_mds9000_fundamentals_config_guide_8x/managing_system_hardware.html?bookSearch=true#concept_BCB88F635E464DFFA2EA73C764411D1C

Review Cisco Networking for a $25 gift card