07-31-2018 11:10 PM - edited 03-08-2019 03:47 PM
Currently one of the AC in data center is down. Could someone please let me know is Cisco 6509 SW doing good here?
Below are the logs of temperature
SW1#show environment
environmental alarms:
no alarms
backplane:
operating clock count: 2
operating VTT count: 3
fan-tray 1:
fan-tray 1 type: WS-C6509-E-FAN
fan-tray 1 mode: restricted-power
fan-tray 1 fan-fail: OK
VTT 1:
VTT 1 OK: OK
VTT 1 outlet temperature: 49C
VTT 2:
VTT 2 OK: OK
VTT 2 outlet temperature: 46C
VTT 3:
VTT 3 OK: OK
VTT 3 outlet temperature: 47C
clock 1:
clock 1 OK: OK, clock 1 clock-inuse: in-use
clock 2:
clock 2 OK: OK, clock 2 clock-inuse: not-in-use
power-supply 1:
power-supply 1 fan-fail: OK
power-supply 1 power-input: AC high
power-supply 1 power-output-mode: high
power-supply 1 power-output-fail: OK
power-supply 2:
power-supply 2 fan-fail: OK
power-supply 2 power-input: AC low
power-supply 2 power-output-mode: low
power-supply 2 power-output-fail: OK
module 1:
module 1 power-output-fail: OK
module 1 outlet temperature: 53C
module 1 inlet temperature: 42C
module 1 device-1 temperature: 42C
module 1 device-2 temperature: 49C
module 2:
module 2 power-output-fail: OK
module 2 outlet temperature: 58C
module 2 inlet temperature: 40C
module 3:
module 3 power-output-fail: OK
module 3 outlet temperature: 55C
module 3 inlet temperature: 42C
module 4:
module 4 power-output-fail: OK
module 4 outlet temperature: 55C
module 4 inlet temperature: 42C
module 6:
module 6 power-output-fail: OK
module 6 outlet temperature: 48C
module 6 inlet temperature: 44C
module 6 device-1 temperature: 50C
module 6 device-2 temperature: 51C
module 6 asic-1 (SSO-1) temp: 44C
module 6 asic-2 (SSO-2) temp: 44C
module 6 asic-3 (SSO-3) temp: 44C
module 6 asic-4 (SSO-4) temp: 44C
module 6 asic-5 (SSA-1) temp: 43C
module 6 asic-6 (HYPERION-1) temp: 43C
module 6 RP outlet temperature: 45C
module 6 RP inlet temperature: 46C
module 6 EARL outlet temperature: 52C
module 6 EARL inlet temperature: 42C
chassis connector rating: 2016.00 Watts (48.00 Amps @ 42V)
module 1
module 1 connector rating: 2016.00 Watts (48.00 Amps @ 42V)
module 1 power consumption: 125.16 Watts ( 2.98 Amps @ 42V)
module 2
module 2 connector rating: 2016.00 Watts (48.00 Amps @ 42V)
module 2 power consumption: 325.50 Watts ( 7.75 Amps @ 42V)
module 3
module 3 connector rating: 2016.00 Watts (48.00 Amps @ 42V)
module 3 power consumption: 295.26 Watts ( 7.03 Amps @ 42V)
module 4
module 4 connector rating: 2016.00 Watts (48.00 Amps @ 42V)
module 4 power consumption: 295.26 Watts ( 7.03 Amps @ 42V)
module 6
module 6 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
module 6 power consumption: 282.24 Watts ( 6.72 Amps @ 42V)
chassis per slot cooling capacity: 70 cfm
ambient temperature: < 55C
module 1 cooling requirement: 70 cfm
module 2 cooling requirement: 70 cfm
module 3 cooling requirement: 70 cfm
module 4 cooling requirement: 70 cfm
module 6 cooling requirement: 35 cfm
SW2#show environment
no alarms
backplane:
operating fan count: 1
fan-tray 1:
fan-tray 1 mode: High-power
VTT 1:
VTT 1 OK: OK
VTT 1 outlet temperature: 47C
VTT 2:
VTT 2 OK: OK
VTT 2 outlet temperature: 40C
VTT 3:
VTT 3 OK: OK
VTT 3 outlet temperature: 44C
clock 1:
clock 2:
power-supply 1:
power-supply 2:
power-supply 2 power-input: AC high
power-supply 2 power-output-mode: high
module 1:
module 1 outlet temperature: 42C
module 1 inlet temperature: 40C
module 1 device-1 temperature: 36C
module 1 device-2 temperature: 44C
module 3:
module 3 inlet temperature: 41C
module 3 aux-1 temperature: 51C
module 3 aux-2 temperature: 48C
module 3 asic-1 temperature: 76C
module 3 asic-2 temperature: 79C
module 3 EARL outlet temperature: 44C
module 3 EARL inlet temperature: 41C
module 6:
module 6 outlet temperature: 41C
module 6 inlet temperature: 37C
module 6 device-1 temperature: 46C
module 6 device-2 temperature: 47C
module 6 asic-1 temperature: 38C
module 6 asic-2 temperature: 38C
module 6 asic-3 temperature: 38C
module 6 asic-4 temperature: 38C
module 6 asic-5 temperature: 38C
module 6 asic-6 temperature: 37C
module 6 RP outlet temperature: 40C
module 6 RP inlet temperature: 40C
module 6 EARL outlet temperature: 46C
module 6 EARL inlet temperature: 37C
chassis connector rating: 1302.00 Watts (31.00 Amps @ 42V)
chassis auxiliary connector rating: 2016.00 Watts (48.00 Amps @ 42V)
module 1
module 3
module 3 power consumption: 444.36 Watts (10.58 Amps @ 42V)
module 6
chassis per slot cooling capacity: 94 cfm
module 3 cooling requirement: 84 cfm
07-31-2018 11:56 PM
07-31-2018 11:58 PM
Is there any recommendation, how much temperature it should hit?
08-01-2018 12:06 AM