Dear Folkz,
I'm getting the below error continuously in N7K platform. Plz help here to resolve this problem.
2013 Jul 16 04:09:29 %PLATFORM-2-MOD_TEMPMINALRM: Xbar-3 reported minor temperature alarm. Sensor=2 Temperature=43 MinThreshold=42
2013 Jul 16 05:45:15 %PLATFORM-2-MOD_TEMPOK: Xbar-3 recovered from minor temperature alarm. Sensor=2 Temperature=41 MinThreshold=42
2013 Jul 16 06:32:18 %PLATFORM-2-MOD_TEMPMINALRM: Xbar-4 reported minor temperature alarm. Sensor=2 Temperature=43 MinThreshold=42
2013 Jul 16 06:35:19 %PLATFORM-2-MOD_TEMPOK: Xbar-4 recovered from minor temperature alarm. Sensor=2 Temperature=41 MinThreshold=42
CORE2# sh environment temperature xbar 3
Temperature:
--------------------------------------------------------------------
Module Sensor MajorThresh MinorThres CurTemp Status
(Celsius) (Celsius) (Celsius)
--------------------------------------------------------------------
xbar-3 Intake (s2) 60 42 39 Ok
xbar-3 Crossbar(s3) 105 95 69 Ok
- Labels:
-
Other Switching
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
07-16-2013 07:07 AM
Kindly clear the air filter to resolve this high temperature issue.
Below are the steps to check and change air filter. http://www.cisco.com/en/US/docs/switches/datacenter/hw/nexus7000/install ation/guide/n7k_replacing.html#wp1109683
HTH
Regards
Inayath
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
07-16-2013 07:10 AM
Dear Shariff,
Thanks For your response !
I'll do the same and update the result shortly :-)