Per Vlan Qos
mohammedrafiq
We have the requirment to rate limit our 1Gig Trunk port into Vlan-7 to 700M and Vlan-3 to 300M,We will use 3560/3750 switch ,and it will be purely L2, no routing.Please advice me best solution.
Pavel Bykov
Level 5
Level 5
Depends if you want to apply it only on onle link or on whole network.
QoS is usually done end-to-end, but if you want it only on one link you can use by setting CoS on incoming ports, and then setting up srr-queues by assigning buffer percentages to the output queues.
Or you can use Policing with MQC. Either by VLAN or per port. Even in Layer 2 there is L3 inspection, so you can use access lists.
If you have VLAN1 with 10.1.1.0/24 and VLAN2 with 10.2.2.0/24, then you can use:
access-list 1 permit 10.1.1.1 0.0.0.255
access-list 2 permit 10.2.2.2 0.0.0.255
class-map match-any vl1
match access-group 1
class-map match-any vl2
match access-group 2
policy-map test
class vl1
police 700000000 20000000
class vl2
police 300000000 9000000
interface gi XX/XX/XX
service-policy input test
refer to this document for buffer management
http://www.cisco.com/en/US/customer/products/hw/switches/ps5528/products_configuration_guide_chapter09186a00803a9b16.html
THANKS,
I will try it,trunk link is between 2 switches, can I do this on both ends?
There are many ways to do it, but if you are going to use the example you would have toapply it on both sides. The example provided can only be used as INPUT service policy, so you need to apply same configuration on both ends, but with reverse ACL.
ACL provided in example only uses source address match. on the other end you need to write it for destination. As in:
access-list 111 permit ip any 10.1.1.1 0.0.0.255
access-list 112 permit ip any 10.2.2.2 0.0.0.255
match access-group 111
match access-group 112
policy-map test
class vl1
class vl2
interface fa 0/41
Check to see if the packets match into your classes with
"show policy-map interface gigaXX/XX/XX" command (the trunk).
Also, you might have to adjust burst sizes, since I have included recommended burst size, which is POLICE_RATE/32. But it may have to be reduced, depending on the switch. You can use smaller bursts, like 1MB (1000000). It will be ok at that speed.
I have applied the config on both side of trunk link, but can only see service policy command on one side, not other, is this normal or bug?.
NOT showing on this sw
CE#sh run int gi1/0/1
Building configuration...
Current configuration : 134 bytes
interface GigabitEthernet1/0/1
switchport trunk allowed
vlan 1,2
switchport mode trunk
showing on this sw.
Switch#sh run int gi1/0/1
Current configuration : 161 bytes
switchport trunk allowed vlan 1,2
service-policy input test <-----------