“LED_FPID: Platform sensor, FAST BLINK event was deasserted
LED_FPID: Platform sensor, OFF event was asserted
LED_FPID: Platform sensor, OFF event was deasserted
LED_FPID: Platform sensor, FAST BLINK event was asserted
LED_HLTH_STATUS: Platform sensor, AMBER was deasserted
LED_HLTH_STATUS: Platform sensor, FAST BLINK event was deasserted
LED_HLTH_STATUS: Platform sensor, GREEN was asserted
LED_HLTH_STATUS: Platform sensor, ON event was asserted
P0V75_DDR3_P1: Voltage sensor, failure event was deasserted
P0V75_DDR3_P1: Voltage sensor, non-recoverable event was deasserted FRU_RAM P1V5_IOH: Voltage sensor for FRU_RAM, non-recoverable event was asserted FRU_RAM P1V5_IOH: Voltage sensor for FRU_RAM, failure event was asserted FRU_RAM P1V1_IOH: Voltage sensor for FRU_RAM, failure event was deasserted FRU_RAM P1V1_IOH: Voltage sensor for FRU_RAM, non-recoverable event was deasserted
- Labels:
-
Unified Computing System (UCS)
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
07-27-2010 12:50 PM
This is a bug with the 5600 series CPUs, the next UCS firmware will fix it. The bug is that the voltage thresholds were set too low, it doesn't affect functionality and can be safely ignored.
Here is the bug ID - CSCth70776