11-30-2010 09:11 AM
High , I used following test-applet to check perdiodically the status of ip sla 199
ip sla 199
icmp-echo 7.192.196.101 source-interface GigabitEthernet0/1
request-data-size 100
threshold 400
ip sla schedule 199 life forever start-time now
event manager applet test
event snmp oid 1.3.6.1.4.1.9.9.42.1.2.9.1.6.199 get-type exact entry-op ge entry-val "0" poll-interval 1 maxrun 200
action 100.0 if $_snmp_oid_val eq 1
action 110.0 set _sla199status "DOWN"
action 120.0 else
action 130.0 set _sla199status "UP"
action 140.0 end
it works fine if the ipsla show as result timeout which result in a value of 1 in the snmp-variable.
if I shutdown the source-interface of ip-sla there are differnt behaviours
on 7200 the
Latest operation return code: timeout
and the snmp-var is 1 which means down
on 3900e
Latest operation return code: Operational failed
and the snmp-var is still 2 which means up
Do I misunderstand anything or could it be a IOS-Bug
Hubert
Solved! Go to Solution.
12-04-2010 06:30 PM
The object 1.3.6.1.4.1.9.9.42.1.2.9.1.6 which is rttMonCtrlOperTimeoutOccurred. If a timeout did not occur, then the value is expected to be 2 (false). Therefore, what you're seeing is expected. You might consider using 1.3.6.1.4.1.9.9.42.1.2.10.1.2.199. If the value of this object is anything other than 1, then an error has occurred.
12-04-2010 06:30 PM
12-06-2010 08:47 AM
Thx for the response, in the meantime I found out myself. I was a little bit confused, because I
thought with M2 this is the correct behaviour (but it seems with M2 this was wrong behav
iour and with M3 now it works correct)
03-05-2025 09:59 PM - edited 03-05-2025 10:11 PM
Hi HUBERT,
What is M2 or M3? Snmpv2 and snmpv3 or slot cards type?
Yossi avrahami