09-03-2021 10:56 AM
I have installed (offline) the new I/O module N7K-F312FQ-25 in the 4th slot of Nexus 7004 device. The 3rd slot is already running with I/O module N7K-M224XP-23L.
When I boot the device, the new module listed with status OK in the show module output. But, the interfaces of the module are not showing up in the interfaces list.
Please guide do we need to configure any command on Nexus 7004 for the module to show up its interfaces.
Your help and support is highly appreciated.
Solved! Go to Solution.
09-03-2021 11:41 PM
In nexus 7000 the interfaces of a new module needs to be allocated first to a specific VDC and only after that you will be able to see them.
switch# conf t switch(config)# vdc <name> switch(config-vdc)# allocate interface ethernet <slot>/<port>-<last-port>
This action needs to be done from default VDC or, if you have one, from admin VDC.
Do a "show run" and search for the VDC part to see how the existing interfaces are allocated.
Stay safe,
Sergiu
09-07-2021 10:42 PM
You need to change your VDC type from supporting F3 as well.
switch(config)# vdc vdc-name switch(config-vdc)# limit-resource module-type m2xl f3
For more details about how to manage your VDC, I would recommend you read the following documentation:
Note: pay attention to table 23 in case in the future you might plan on doing other mixes between different LC models.
Stay safe,
Sergiu
09-03-2021 03:29 PM
is this VDC, have you allocated the resources ? can you show the module output ?
09-03-2021 11:41 PM
Stay safe,
Sergiu
09-06-2021 02:07 PM
I tried to add interface in the current VDC and received the below error
ERROR: 1 or more interfaces are from a module of type not supported by this vdc
New Module installed is N7K-F312FQ-25 and
in the VDC configuration, limit resource command has supported module type as "limit-resource module-type m1 f1 m1xl m2xl".
Should I add any module-type in the limit resource command for the module "N7K-F312FQ-25".
Kindly help.
09-06-2021 04:32 PM
Can you post the complete output of show modules
09-07-2021 08:17 AM
Hi..
FYR...
r02# show module
Mod Ports Module-Type Model Status
1 0 Supervisor Module-2 N7K-SUP2E active *
2 0 Supervisor Module-2 N7K-SUP2E ha-standby
3 24 10 Gbps Ethernet Module N7K-M224XP-23L ok
4 12 10/40 Gbps Ethernet Module N7K-F312FQ-25 ok
Mod Sw Hw
1 7.3(3)D1(1) 1.0
2 7.3(3)D1(1) 6.2
3 7.3(3)D1(1) 1.1
4 7.3(3)D1(1) 1.1
Mod Online Diag Status
1 Pass
2 Pass
3 Pass
4 Pass
* this terminal session
r02#
09-07-2021 10:42 PM
Stay safe,
Sergiu
09-24-2021 02:18 PM
Hi Sergiu,
Thanks for your support. As you instructed, I changed the module type in the VDC and didn't encounter any issues. Following that, I allocated the new module interfaces in the current VDC. Everything is working fine.
As the devices are in production environment, it took time to make changes.
Mohamed Ali