05-04-2017 04:59 AM - last edited on 03-25-2019 03:10 PM by ciscomoderator
Hi
I am having the same issue we have checked the power cable and tested it and it it is okay but still I am having same issue with power supply 1
nvironmental alarms:
system minor alarm on power-supply 1 power-output-fail (raised 1d00h ago)
backplane:
operating clock count: 2
operating VTT count: 3
fan-tray 1:
fan-tray 1 type: WS-C6506-E-FAN
fan-tray 1 mode: Restricted-power
fan-tray 1 fan-fail: OK
VTT 1:
VTT 1 OK: OK
VTT 1 outlet temperature: 37C
VTT 2:
VTT 2 OK: OK
VTT 2 outlet temperature: 34C
VTT 3:
VTT 3 OK: OK
VTT 3 outlet temperature: 51C
clock 1:
clock 1 OK: OK, clock 1 clock-inuse: in-use
clock 2:
clock 2 OK: OK, clock 2 clock-inuse: not-in-use
power-supply 1:
power-supply 1 power-output-fail: failed
power-supply 2:
power-supply 2 fan-fail: OK
power-supply 2 power-input: AC high
power-supply 2 power-output-mode: high
power-supply 2 power-output-fail: OK
module 1:
module 1 power-output-fail: OK
module 1 outlet temperature: 31C
module 1 inlet temperature: 27C
module 3:
module 3 power-output-fail: OK
module 3 outlet temperature: 39C
module 3 inlet temperature: 33C
module 3 device-1 temperature: 29C
module 3 device-2 temperature: 36C
module 3 aux-1 temperature: 34C
module 3 aux-2 temperature: 34C
module 5:
module 5 power-output-fail: OK
module 5 outlet temperature: 40C
module 5 inlet temperature: 30C
module 5 device-1 temperature: 42C
module 5 device-2 temperature: 43C
module 5 asic-1 (SSO-1) temp: 29C
module 5 asic-2 (SSO-2) temp: 29C
module 5 asic-3 (SSO-3) temp: 29C
module 5 asic-4 (SSO-4) temp: 29C
module 5 asic-5 (SSA-1) temp: 29C
module 5 asic-6 (HYPERION-1) temp: 29C
module 5 RP outlet temperature: 33C
module 5 RP inlet temperature: 32C
module 5 EARL outlet temperature: 44C
module 5 EARL inlet temperature: 30C
chassis connector rating: 2016.00 Watts (48.00 Amps @ 42V)
module 1
module 1 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
module 1 power consumption: 84.00 Watts ( 2.00 Amps @ 42V)
module 2
module 2 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
module 2 power consumption: 103.74 Watts ( 2.47 Amps @ 42V)
module 3
module 3 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
module 3 power consumption: 171.78 Watts ( 4.09 Amps @ 42V)
module 5
module 5 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
module 5 power consumption: 282.24 Watts ( 6.72 Amps @ 42V)
chassis per slot cooling capacity: 70 cfm
ambient temperature: < 55C
module 1 cooling requirement: 30 cfm
module 2 cooling requirement: 30 cfm
module 3 cooling requirement: 30 cfm
module 5 cooling requirement: 35 cfm
Can anybody assist me on this?
Regards,
Jason
05-04-2017 06:17 AM
does the power supply have a red led on it , did you try reseat it physically ?
do you have a spares PS you can test in that slot , it only needs 1 to run there oir so they can be removed once 1 is left in place while its operational to test
05-04-2017 06:35 AM
Hi Mark,
No light at all even fan not working I tried exchanging the power chord from 1 to 2 still have the same issue luckily we have 2nd power supply which we are running right now.
Regards,
Jason
05-04-2017 07:03 AM
sounds like PS is dead they do go but not very often , replaced one recently on a 65
my next move if it was in my place would be get another PS in the slot it will rules out everything ,if that works you know its most likely the PS , unfortunately if you have no other spare , you may have to have a power down and flip the working and non working around in a maintenance window that's planned or buy another PS
theres no quick config thing here that's going to help , this is some form of layer 1 issue , the fact you tested the cabling really makes me think PS is gone or blown , usually if it has an issue but can be fixed the light goes from green to red and then you can re-seat it and it will go green again , the fact theres no light on the PS on a working cable doesn't sound good
is your chassis under support the power supply's are covered along with the modules so you could request a replacement off your support vendor instead of buying one , or ask them can you borrow one as a test to rule out current issue
05-04-2017 07:07 AM
Hi Mark,
Actually now we are looking for the PS including my Ethernet module which is also down at the moment luckily again I have redundant core switch with Ethernet but most of the cisco vendor I have contacted they told me that my modules are old and now EOS from Cisco
Regards,
Jason
05-04-2017 07:28 AM
ah ok its too old to support , it about 5 grand a year to support a 6500 anyway , I just budgeted a few of through my var , there not cheap devices , but saying that there not the newest anymore and you could pick up a power supply for a couple of hundred online to test with or replace
always good to have plenty of spares when not under support
05-04-2017 07:32 AM
Hi Mark,
Yes I have coordinated with other vendor even reconditioned modules can be considered as of the moment because we don't have any options specially my Ethernet module showing this message:
2 WS-X6148-GE-TX 103.74 2.47 - - on off (FRU-power failed)
Regards,
Jason
05-04-2017 07:47 AM
Looks like this has popped up before on a 6513 , may not be enough power to run it until the PS fixed or else that's gone too , hopefully not
https://supportforums.cisco.com/discussion/10854816/cisco-6513-c6kpwr-sp-4-disabled-power-module-slot-3-set-fru-power-failed
05-04-2017 07:50 AM
I think the PS was long gone and the Ethernet module was running last few days only yesterday it went down. My core 2 is also running on 1 PS but Ethernet module is working
05-04-2017 07:53 AM
try restart it with
hw-module module x boot
or
(config)#power enable switch x module x
if it doesn't come up with those command its probably gone
05-04-2017 07:58 AM
yup already did the command
(config)#power enable module 2
still have the same result.