11-15-2013 10:33 AM - edited 03-04-2019 09:35 PM
Hello guys,
Basically I looked in every book from cisco.com about ASR1000 and could not find how to interpret some abbreviated names when viewing the temperatures and sensors info.
I am interested in the following:
what is "Left"? the location of the sensor or anything else?
the same goes to center and right
Temp: Left 0 Normal 37 Celsius
Temp: Center 0 Normal 33 Celsius
Temp: Asic1 0 Normal 42 Celsius
Temp: Right 0 Normal 25 Celsius
Also these
Temp: Inlet F0 Normal 35 Celsius
Temp: Asic1 F0 Normal 51 Celsius
Temp: Exhaust1 F0 Normal 48 Celsius
Temp: Exhaust2 F0 Normal 48 Celsius
Temp: Asic2 F0 Normal 42 Celsius
Please, help me to find their meanings or let me know where can I read about it.
Thanks as usual!!!
11-15-2013 03:47 PM
Look at the temperature readings.
Notice how "Right" is cooler compared to "Left"?
This means that air is "pulled" from the right, goes through the ASIC (which is always hot, by the way) and expelled to the "Left". This is how the ASR is being cooled.
11-15-2013 09:18 PM
Ooh Leo, thank you very much, I see now!!! You know I figured out the other abbreviations P0,P1, F0 and R0, that was not very difficult.. Thanks for the clarification again, many things are clearer for me now))