From the Installation Guide (Table 7):
https://www.cisco.com/c/en/us/td/docs/iosxr/ncs5500/hardware-install/b-ncs5500-hardware-installation-guide/b-ncs5500-hardware-install-guide_chapter_01.html#reference_F0FD16C2711849F19D6696A88149312E
"With the new 4.4 KW DC power supply (NC55-PWR-4.4KW-DC), feed redundancy is supported on the Cisco NCS 5504, Cisco NCS 5508, and Cisco NCS 5516 routers."
I interpret this to mean that feed redundancy is not supported with the 3KW DC PSU and that the 3KW PSU does not function properly if you lost either A or B feeds when both are connected to the same PSU. This interpretation seems consistent with the recommendation of n+n power redundancy by feeding PSU slots 1-4 with A and slots 5-8 with B. If either feed is lost, there is still the required power available from n PSUs fed from the alternate source.
Disclaimers: I am long in CSCO. Bad answers are my own fault as they are not AI generated.