Hi dears
Our company buy new Cisco 6506_e series switch. When i turn on first time then i see this fan error and i did some show command:
Router#show power
system power redundancy mode = redundant
system power total = 3795.12 Watts (90.36 Amps @ 42V)
system power used = 1621.20 Watts (38.60 Amps @ 42V)
system power available = 2173.92 Watts (51.76 Amps @ 42V)
Power-Capacity PS-Fan Output Oper
PS Type Watts A @42V Status Status State
---- ------------------ ------- ------ ------ ------ -----
1 WS-CAC-4000W-INT 3795.12 90.36 OK OK on
2 WS-CAC-4000W-INT 3795.12 90.36 OK OK on
Pwr-Allocated Oper
Fan Type Watts A @42V State
---- ------------------ ------- ------ -----
1 WS-C6506-E-FAN 140.70 3.35 failed
Pwr-Requested Pwr-Allocated Admin Oper
Slot Card-Type Watts A @42V Watts A @42V State State
---- ------------------ ------- ------ ------- ------ ----- -----
1 WS-X6824-SFP 204.54 4.87 204.54 4.87 on on
2 WS-X6848-GE-TX 404.88 9.64 404.88 9.64 on on
5 VS-SUP2T-10G 435.54 10.37 435.54 10.37 on on
6 (Redundant Sup) - - 435.54 10.37 - -
system auxiliary power mode = off
system auxiliary power redundancy operationally = non-redundant
system primary connector power limit = 7266.00 Watts (173.00 Amps @ 42V)
system auxiliary connector power limit = 10500.00 Watts (250.00 Amps @ 42V)
system primary power used = 1621.20 Watts (38.60 Amps @ 42V)
system auxiliary power used = 0 Watt
-------------------------------------------------------------------------------------------------------------------------------------
Router#show environment cooling
fan-tray 1:
fan-tray 1 type: WS-C6506-E-FAN
fan-tray 1 mode: High-power
fan-tray 1 fan-fail: failed
chassis per slot cooling capacity: 94 cfm
ambient temperature: < 55C
module 1 cooling requirement: 70 cfm
module 2 cooling requirement: 70 cfm
module 5 cooling requirement: 84 cfm
-------------------------------------------------------
Router#sh environment status
backplane: operating clock count: 2
operating VTT count: 3
operating fan count: 1
fan-tray 1:
fan-tray 1 type: WS-C6506-E-FAN
fan-tray 1 mode: High-power
fan-tray 1 fan-fail: failed
VTT 1:
VTT 1 OK: OK
VTT 1 outlet temperature: 27C
VTT 2:
VTT 2 OK: OK
VTT 2 outlet temperature: 24C
VTT 3:
VTT 3 OK: OK
VTT 3 outlet temperature: 22C
clock 1:
clock 1 OK: OK, clock 1 clock-inuse: in-use
clock 2:
clock 2 OK: OK, clock 2 clock-inuse: not-in-use
power-supply 1:
power-supply 1 fan-fail: OK
power-supply 1 power-input: AC high
power-supply 1 incompatible with fan: OK
power-supply 1 power-output-fail: OK
power-supply 2:
power-supply 2 fan-fail: OK
power-supply 2 power-input: AC high
power-supply 2 incompatible with fan: OK
power-supply 2 power-output-fail: OK
module 1:
module 1 power-output-fail: OK
module 1 outlet temperature: 25C
module 1 inlet temperature: 23C
module 1 device-1 temperature: 21C
module 1 device-2 temperature: 26C
module 1 EARL outlet temperature: 28C
module 1 EARL inlet temperature: 23C
module 2:
module 2 power-output-fail: OK
module 2 outlet temperature: 27C
module 2 inlet temperature: 21C
module 2 EARL outlet temperature: 28C
module 2 EARL inlet temperature: 22C
module 5:
module 5 power-output-fail: OK
module 5 outlet temperature: 34C
module 5 inlet temperature: 21C
module 5 device-1 temperature: 29C
module 5 device-2 temperature: 31C
module 5 asic-1 temperature: 50C
module 5 asic-2 temperature: 35C
module 5 asic-4 temperature: 51C
module 5 asic-5 temperature: 45C
module 5 asic-7 temperature: 45C
module 5 asic-8 temperature: 54C
module 5 RP outlet temperature: 29C
module 5 RP inlet temperature: 25C
module 5 RP device-1 temperature: 42C
module 5 EARL outlet temperature: 29C
module 5 EARL inlet temperature: 22C
module 5 EARL device-1 temperature: 52C
module 5 EARL device-2 temperature: 53C--
-------------------------------------------------------------
at the begining :
Oct 7 10:47:54.299: %C6KPWR-4-PSREDUNDANTBOTHSUPPLY: in power-redundancy mode, system is operating on both power supplies.
*Oct 7 10:47:55.347: %C6KENV-4-FANHPMODE: Fan-tray 1 is operating in high power mode
*Oct 7 10:48:00.835: %FABRIC-5-FABRIC_MODULE_ACTIVE: The Switch Fabric Module in slot 5 became active.
*Oct 7 10:48:03.211: %C6KENV-4-FANTRAYFAILED: fan tray 1 failed
1.First i think that this is a high power problem. we must be decrease the power? am i rigth?
2. As you see power mode is High-power.
i know that e series default power mode is restricted but here is high power.
is it possbly i chanege the power mode to restricted mode? if yes, which command i must be type?
please help me.
thanks.
10-09-2013 08:20 AM
Hello Teymur,
the high power mode, at least for me, is normal mode in our DataCenter's.
I don't believe that your problem is the power mode but yes that your fan is broken (stopped).
I recommend you to open RMA directly for that FAN.
Here you have an output from our Catalyst 6500 (in VSS),and they are working perfectly:
show power
system power redundancy mode = redundant
system power total = 5771.64 Watts (137.42 Amps @ 42V)
system power used = 3096.66 Watts (73.73 Amps @ 42V)
system power available = 2674.98 Watts (63.69 Amps @ 42V)
Power-Capacity PS-Fan Output Oper
PS Type Watts A @42V Status Status State
---- ------------------ ------- ------ ------ ------ -----
1 WS-CAC-6000W 5771.64 137.42 OK OK on
2 WS-CAC-6000W 5771.64 137.42 OK OK on
Pwr-Allocated Oper
Fan Type Watts A @42V State
---- ------------------ ------- ------ -----
1 WS-C6509-E-FAN 210.00 5.00 OK
Pwr-Requested Pwr-Allocated Admin Oper
Slot Card-Type Watts A @42V Watts A @42V State State
---- ------------------ ------- ------ ------- ------ ----- -----
1 WS-X6724-SFP 125.16 2.98 125.16 2.98 on on
2 WS-X6748-GE-TX 325.50 7.75 325.50 7.75 on on
3 WS-X6748-GE-TX 325.50 7.75 325.50 7.75 on on
4 WS-X6748-GE-TX 325.50 7.75 325.50 7.75 on on
5 VS-S720-10G 338.10 8.05 338.10 8.05 on on
6 VS-S720-10G 338.10 8.05 338.10 8.05 on on
7 WS-X6748-GE-TX 325.50 7.75 325.50 7.75 on on
8 WS-X6748-GE-TX 325.50 7.75 325.50 7.75 on on
9 WS-X6716-10GE 457.80 10.90 457.80 10.90 on on
system auxiliary power mode = off
system auxiliary power redundancy operationally = non-redundant
system primary connector power limit = 10920.00 Watts (260.00 Amps @ 42V)
system auxiliary connector power limit = 10500.00 Watts (250.00 Amps @ 42V)
system primary power used = 3096.66 Watts (73.73 Amps @ 42V)
system auxiliary power used = 0 Watt
show environment cooling
switch 1 fan-tray 1:
switch 1 fan-tray 1 type: WS-C6509-E-FAN
switch 1 fan-tray 1 mode: High-power
switch 1 fan-tray 1 fan-fail: OK
chassis per slot cooling capacity: 94 cfm
switch 1 module 1 cooling requirement: 70 cfm
switch 1 module 2 cooling requirement: 70 cfm
switch 1 module 3 cooling requirement: 70 cfm
switch 1 module 4 cooling requirement: 70 cfm
switch 1 module 5 cooling requirement: 35 cfm
switch 1 module 6 cooling requirement: 35 cfm
switch 1 module 7 cooling requirement: 70 cfm
switch 1 module 8 cooling requirement: 70 cfm
switch 1 module 9 cooling requirement: 84 cfm
Best Regards.