Hey, I started monitoring our catalyst 2960 / Nexus 5000 Switches the temperature readings I get from the Catalyst switches is between 40° and 45°C. The official documentation states a maximum operation temperature of 45°C
(http://www.cisco.com/en/US/docs/switches/lan/catalyst2960x/hardware/installation/guide/b_c2960x_hig_appendix_0100.html).
But what exacly is the operation temperature? Is it the Air-Temp in the Rack or the Temperature reading I get from the snmpwalk? The threshold values on the switch are a lot higher - that indicates that the operation temperature is the air-temp.
The Nexus Switches we have are cooled Back to front - but the psu´s are front to back. The temperature reading i get is at 50°C and the PSU Temp is at about 26/27°. The maximum operation temperature is 40°C!!
(http://www.cisco.com/c/en/us/td/docs/switches/datacenter/nexus5000/hw/installation/guide/nexus_5000_hig/techspec.html)
Is the Temperature so high because of the Airflow?