Power should provided for Nexus 7010 in my Rack

lcd_shouldit
Level 1
Level 1

Hi, there are 3 7.5Kw power supply in my Nexus 7010.

and the redundant mode is REDUNDANT.

So what is the exactly power should I provide for this Nexus in my rack.

7.5 x 3 = 22.5 Kw ?

Thanks a lot!

3 Replies 3

Reza Sharifi
Hall of Fame
Hall of Fame

That is correct. 22.5 is the max based on how many blades and sups you have in the chassis.  Each power supply comes with 2 outputs.  For load sharing, it is good idea if you can connect each output to a different PDU. You need c19/c20 power cords to connect the PSUs to the PDUs.

HTH

Hello,

I need to correct Reza here. With current mode of redundancy you will get 11,250W:

Redundant mode means

redundant

Input Source (GRID) + Power Supply Redundancy - The available power is the lesser of the available power for the power supply mode and input source voltage. The difference (50%) is reserved for backup.

http://www.cisco.com/en/US/docs/switches/datacenter/sw/best_practices/cli_mgmt_guide/init_config.html#wp1053349

As per table 5  in the link below 3 PS will give 11.250 in this mode:

http://www.cisco.com/en/US/prod/collateral/switches/ps9441/ps9402/ps9512/Data_Sheet_C78-437761_ps9402_Products_Data_Sheet.html

Niko

HTH,
Niko

Hi, thanks so much!

So, 3 PS will give me 11,250 W in this mode, which is the output.

How about the input, Should I prepare 7.5 x 3 = 22.5Kw for this Nexus ?