The RPS 2300
• Innovative power architecture delivers a cost-effective RPS that can connect up to six devices and can actively back-up up to two devices simultaneously, thereby reducing the redundant power cost per device.
why does it say "can connect up to six devices and can actively back-up up to two devices simultaneously"???
If I have 3 switches connected, and all 3 of them lose their AC power coming in, will this device continue to operate all 3 switches?
Manuel Garcia
Solved! Go to Solution.
- Labels:
-
Other Switching
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
05-26-2011 07:53 PM
Hi Manuel,
Yep it says " Innovative power architecture delivers a cost-effective RPS that can connect up to six devices and can actively back-up up to two devices simultaneously, thereby reducing the redundant power cost per device."
You said."If I have 3 switches connected, and all 3 of them lose their AC power coming in, will this device continue to operate all 3 switches?"
So you can have up to six devices connected to the unit, the Redundant Power Supply 2300 (RPS2300) can only backup two power supply failures at once.
So, as you say in your example you have three switches connected and all three loose AC power....well if the Redundant Power Supply 2300 (RPS2300) is also on a UPS, the RPS2300 will backup maximum of two power supplies, so only one switch will be down..
But it is designed to backup the POWER SUPPLY hardware and not really the AC power of certain supported switches. It is a product to backup the Power supply hardware within a switch , and not really the AC power coming into the switch.
The Redundant Power Supply 2300 (RPS2300) ishould not be thought of as a UPS, it should be thought of as a redundant power supply that will backup, maximum two power supplies within two switches at once.
Notice the datasheet that you referred us to show the application where a UPS is used to backup BOTH the RPS2300 and the Swithes.
By the way, the odds of two power supplies failing at once in two seperate switches is remote.
The probablility of losing three power supplies at once due to hardware faulure within three switches is very remote.
regards Dave
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
05-26-2011 07:53 PM
Hi Manuel,
Yep it says " Innovative power architecture delivers a cost-effective RPS that can connect up to six devices and can actively back-up up to two devices simultaneously, thereby reducing the redundant power cost per device."
You said."If I have 3 switches connected, and all 3 of them lose their AC power coming in, will this device continue to operate all 3 switches?"
So you can have up to six devices connected to the unit, the Redundant Power Supply 2300 (RPS2300) can only backup two power supply failures at once.
So, as you say in your example you have three switches connected and all three loose AC power....well if the Redundant Power Supply 2300 (RPS2300) is also on a UPS, the RPS2300 will backup maximum of two power supplies, so only one switch will be down..
But it is designed to backup the POWER SUPPLY hardware and not really the AC power of certain supported switches. It is a product to backup the Power supply hardware within a switch , and not really the AC power coming into the switch.
The Redundant Power Supply 2300 (RPS2300) ishould not be thought of as a UPS, it should be thought of as a redundant power supply that will backup, maximum two power supplies within two switches at once.
Notice the datasheet that you referred us to show the application where a UPS is used to backup BOTH the RPS2300 and the Swithes.
By the way, the odds of two power supplies failing at once in two seperate switches is remote.
The probablility of losing three power supplies at once due to hardware faulure within three switches is very remote.
regards Dave
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
05-31-2011 12:05 PM
Hi David
Thanks for your Answer,
It's possible to have other model of RPS can allow the three switches up the switches are cisco WS-C2960-24TT-L
Manuel
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
05-31-2011 12:28 PM
Hi Manuel.
I checked out the Q&A on the RPS2300; URL;
and found the following chart;
Table 1. Number of Switches Actively Backed Up by the Cisco RPS 2300
Cisco RPS 2300 Power Supply Configuration | ||||
1 x 750W | 2 x 750W | 1 x 1150W | 2 x 1150W | |
Cisco Catalyst 3750-E or 3560-E switches with 1150W PS | Not supported | 1 | 1 | 2 |
All other supported network devices | 1 | 2 | 1 | 2 |