Hello,
We have a switch 4507R_E with two processor V-10GE: one active and the othe as standby.
The problem we have is that the standby processor is in disable state.
This is the sh module of the switch:
4507R_E#sh module
Chassis Type : WS-C4507R-E
Power consumed by backplane : 40 Watts
Mod Ports Card Type Model Serial No.
---+-----+--------------------------------------+------------------+-----------
1 48 10/100/1000BaseT (RJ45)V, Cisco/IEEE WS-X4548-GB-RJ45V JAE1419006P
2 6 1000BaseX (GBIC) WS-X4306-GB JAE14190JHL
3 Supervisor
4 6 Sup V-10GE 10GE (X2), 1000BaseX (SFP) WS-X4516-10GE JAE14190FG9
5 6 1000BaseX (GBIC) WS-X4306-GB JAE14190JHM
M MAC addresses Hw Fw Sw Status
--+--------------------------------+---+------------+----------------+---------
1 5475.d0a2.7340 to 5475.d0a2.736f 5.0 Ok
2 001e.7ad1.95cc to 001e.7ad1.95d1 4.4 Ok
3 Unknown Unknown Unknown Other
4 5475.d04c.b2c6 to 5475.d04c.b2cb 5.2 12.2(31r)SGA 12.2(54)SG Ok
5 001b.d4fd.a9f2 to 001b.d4fd.a9f7 4.4 Ok
Mod Redundancy role Operating mode Redundancy status
----+-------------------+-------------------+----------------------------------
3 Standby Supervisor SSO Disabled
4 Active Supervisor SSO Active
4507R_E#
Can some body tell us which is the procedure to put tha standby processor to active instead of disable?
What is the normal state of standby processor?
Are there some link where we can see in more detail this procedure?
Attentively,
Roger Fernando Majo Z.
Ing. Soporte NOC y Proyectos
Telefono: (511) 513-2960 Anexo: 52993
Email: rmajos@gromero.com.pe
Celular: 996918812
RPM: #263689
Fax: (511) 221.0500
Direccion: Av. Camino Real 390. Piso 13
Torre Central Of.301. San Isidro, Lima-Peru
www.sitel.com.pe
Solved! Go to Solution.
05-23-2011 10:54 AM
Hi,
No I don't want you to reset it. I mean "reseat". You just pull Supervisor off and then push it back in. And then you just try the steps I told you to verify it.
HTH,
Toshi
05-22-2011 09:50 PM
Hi,
It's not normal.
What is the normal state of standby processor?
A: The output has to be as follows:
Mod Redundancy role Operating mode Redundancy status
----+-------------------+-------------------+----------------------------------
3 Standby Supervisor SSO Standby hot
4 Active Supervisor SSO Active
#########################
Can some body tell us which is the procedure to put tha standby processor to active instead of disable?
A: You may need to carefully reseat SupV-10GE on module 3.
Step 1 Ensure that the LED labeled Status is green (module operational).
Step 2 When the switch is online, enter the show module command. Verify that the system acknowledges the new module and that the module's status is good.
Step 3 If the module is not operational, reseat it. If the module is still not operational, contact your customer service representative.
HTH,
Toshi
05-23-2011 07:15 AM
Hi Toshi,
Whish is the procedure to reset carefully the processor V-10GE in slot 3?
Do we must connect via console cable to the supervisor and then use the command: reset ?
Will affect this operation the operation of the switch 4507R_E? (this switch is the CORE of a computer center).
Waiting your sooner answer.
Attentively.
Roger Majo
Lima-Peru.
05-23-2011 09:37 AM
Hi,
Just try to reseat SupV-10GE on module3.
All Catalyst 4500 series switches support hot swapping, which lets you install, remove, replace, and rearrange supervisor engines and switching modules without powering the system off. When the system detects that a switching module has been installed or removed, it runs diagnostic and discovery routines automatically, acknowledges the presence or absence of the module, and resumes system operation with no operator intervention.
To check the status of the module, follow these steps:
Step 1 Ensure that the LED labeled Status is green (module operational)
Step 2 When the switch is online, enter the show module command. Verify that the system acknowledges the new module and that the module's status is good.
Step 3 If the module is not operational, reseat it. If the module is still not operational, contact your customer service representative.
HTH,
Toshi
05-23-2011 10:41 AM
Toshi,
Thanks for your answer.
But i have one question about the procedure to reset the processor in standby:
Waiting your sooner asnwer.
Attn.
Roger Majo
05-23-2011 10:54 AM
Hi,
No I don't want you to reset it. I mean "reseat". You just pull Supervisor off and then push it back in. And then you just try the steps I told you to verify it.
HTH,
Toshi
05-23-2011 03:49 PM
Toshi,
That is right.
Today I am going to reseat the module and follow the procedure you told me.
I am going to tell you the results.
Thanks.
Roger Majo
05-26-2011 07:41 AM
Toshi,
I reseated the processor standby module and it is in standby_hot instead of disable.
I used many command to confirm this is state and id o.k.
Thanks very much.
Roger Majo