%SYS-2-FAN_INSUFFICIENTCOOLING Error Message -
Mike A.
Hello -
Trying to add a 6708 10G-3C blade to an existing 6509-E chassis with 6509-E-FAN, but I am getting the below error message.  My understanding is that the fan is supposed to automatically recognize the 67xx blade that requires 84 cfm and move from restricted power mode to high power but that didn't happen (chassis is limited to 70 cfm per slot currently).  We've re-seated the fan and reloaded the switch - still no luck.  Is this a power supply issue (currently running dual 2500W)?  We ran the power calculator and didn't see any issues.
Thoughts/suggestions?  Thanks.
~Mike
2003 Dec 16 21:32:53 %SYS-2-FAN_INSUFFICIENTCOOLING: Module 1 cannot be adequately cooled
2003 Dec 16 21:32:53 %SYS-5-MOD_PWRDENY: Power denied to module 1
2003 Dec 16 21:32:53 %SYS-5-MOD_INSERT: Module 1 has been inserted
Here are the environment information:
Environmental Status (. = Pass, F = Fail, U = Unknown, N = Not Present)
  PS1: .     PS2: .     PS1 Fan: .     PS2 Fan: .
  Chassis-Ser-EEPROM: .     Fan1: .
  Clock(A/B): A         Clock A: .     Clock B: .
  VTT1: .    VTT2: .    VTT3: .
                  Intake          Exhaust         Device 1        Device 2
Slot            Temperature     Temperature     Temperature     Temperature
3               23C(50C,65C)    31C(85C,100C)   N/A             N/A
5               20C(45C,60C)    25C(50C,65C)    29C(55C,70C)    29C(55C,70C)
6               20C(45C,60C)    25C(50C,65C)    27C(55C,70C)    28C(55C,70C)
7               25C(45C,60C)    25C(55C,70C)    N/A             N/A
9               24C(45C,60C)    26C(55C,70C)    N/A             N/A
5  (Switch-Eng) 21C(45C,60C)    32C(60C,75C)
5  (MSFC)       24C(50C,65C)    24C(50C,65C)
6  (Switch-Eng) 21C(45C,60C)    30C(60C,75C)
6  (MSFC)       23C(50C,65C)    23C(50C,65C)
7  (VDB)         23C(75C,90C)    25C(70C,85C)    25C(75C,90C)    N/A
9  (VDB)         24C(75C,90C)    25C(70C,85C)    25C(75C,90C)    N/A
Chassis Modules
VTT1: 28C(100C,115C)
VTT2: 29C(100C,115C)
VTT3: 36C(100C,115C)
PS1 WS-CAC-2500W AC with 1 input(s) and 2 output mode(s)
  Capacity               :
    Mode1                : 1153.32 Watts ( 27.46 Amps @42V)
    Mode2 [operational]  : 2331.00 Watts ( 55.50 Amps @42V)
  Capabilities
    Floating power       : No
    Remote reset         : No
    Input configuration  : No
  Status
    Online               : Yes
    Used                 : Yes
    Output status        : Ok
      PS                 : Ok
      PS Fan             : Ok
    IVM mode             : High AC
PS2 WS-CAC-2500W AC with 1 input(s) and 2 output mode(s)
  Capacity               :
  Capabilities
    Floating power       : No
    Remote reset         : No
  Status
    Online               : Yes
    Used                 : Yes
    Output status        : Ok
      PS                 : Ok
      PS Fan             : Ok
    IVM mode             : High AC
PS Configuration : PS1 and PS2 in Redundant Configuration.
Total Power Available                        :  2331.00 Watts ( 55.50 Amps @42V)
Total Power Chassis Limit                    : 14700.00 Watts (350.00 Amps @42V)
Total Power Chassis Recommended              : 14700.00 Watts (350.00 Amps @42V)
Total Power Available for Line Card Usage    :  2331.00 Watts ( 55.50 Amps @42V)
Total Power Drawn From the System            :  1157.52 Watts ( 27.56 Amps @42V)
Total Power Drawn by the Chassis             :     0.00 Watt
Total Power Drawn by the modules             :   997.92 Watts ( 23.76 Amps @42V)
Total Inline Power Drawn From the System     :    88.50 Watts (  2.11 Amps @42V)
Total Power Reserved as localpool for modules:    71.40 Watts (  1.70 Amps @42V)
Remaining Power in the System                :  1173.48 Watts ( 27.94 Amps @42V)
Configured Default Inline Power per port     :    15.40 Watts (  0.37 Amps @42V)
Slot power Requirement/Usage :
Slot Model                   Power Requested Power Allocated CardStatus
                             Watts    A @42V Watts    A @42V
1    Unknown                   375.06   8.93     0.00   0.00 power-deny
3    WS-X6516-GBIC             142.80   3.40   142.80   3.40 ok
5    WS-SUP720-BASE            315.00   7.50   315.00   7.50 ok
6    WS-SUP720-BASE            315.00   7.50   315.00   7.50 standby
7    WS-X6148A-GE-45AF         112.56   2.68   112.56   2.68 ok
9    WS-X6148A-GE-45AF         112.56   2.68   112.56   2.68 ok
Slot Inline Power Requirement/Usage :
Slot Sub-Model           Total Allocated   Max H/W Supported  Max H/W Supported
                         To Module (Watts) Per Module (Watts) Per Port (Watts)
7    WS-F6K-48-AF        17.701            850.08             15.400
9    WS-F6K-48-AF        70.804            850.08             15.400
Chassis per slot cooling capacity : 70 cfm
Fan tray(s) cooling capacity :
Fan  Model               Ver Cooling  Ambient FanStatus
                             capacity temp
1    WS-C6509-E-FAN        2  630 cfm     55C ok
Slot cooling requirement :
Slot CardType            Cooling
1    Unknown              84 cfm
3    WS-X6516-GBIC        30 cfm
5    WS-SUP720-BASE       35 cfm
6    WS-SUP720-BASE       35 cfm
7    WS-X6148A-GE-45AF    35 cfm
9    WS-X6148A-GE-45AF    35 cfm
Chassis connector rating :  1260.00 Watts ( 30.00 Amps @42V)
Slot connector rating :
Slot CardType            ConnectorRating
                         Watts    A @42V
1    Unknown              2016.00  48.00
3    WS-X6516-GBIC        1260.00  30.00
5    WS-SUP720-BASE       1260.00  30.00
6    WS-SUP720-BASE       1260.00  30.00
7    WS-X6148A-GE-45AF    1092.00  26.00
9    WS-X6148A-GE-45AF    1092.00  26.00
Hi Mike,
If you don't have the card and you want to upgrade, I recommend you go to a different sup like Sup-720-VS or Sup-2T, as all of these sups are end-of-life except Sup-2T and you don't want to purchase something that is already end-of-life.
Have a look at Sup-2T data sheet and let me know if you need more info:
http://www.cisco.com/c/en/us/products/collateral/interfaces-modules/catalyst-6500-series-supervisor-engine-2t/data_sheet_c78-648214.html
Reza Sharifi
Since your sup is 720 and not VS, do you have a PFC card installed?
See table-1 in this link for sup compatibility.
http://www.cisco.com/c/en/us/products/collateral/switches/catalyst-6500-series-switches/product_data_sheet09186a00801dce34.html
Hi Reza - thank you for the email.  No, I don't believe that we do.  Would you recommend upgrading to the Sup720-3B for the above hardware config?
Hi Mike,