08-06-2018 01:19 AM - edited 03-08-2019 03:50 PM
I am experiencing this problem, can anybody help me to solve this issue.The temperature in the data centre is 20 degree celcius.
I have attached the logs of it, please share a solution for it.
#show environment
warning alarm: slot 3 has exceeded the warning temperature for 49h 05m 55s
Module Sensor Temperature Status
------+--------------------------+--------------------+------------
3 air inlet 37C (51C,65C,68C) ok
3 air outlet 66C (69C,83C,86C) warning
4 air inlet 40C (51C,65C,68C) ok
4 air outlet 57C (69C,83C,86C) ok
Power Fan Inline
Supply Model No Type Status Sensor Status
------ ---------------- --------- ----------- ------- -------
PS1 PWR-C45-1400AC AC 1400W good good n.a.
PS2 PWR-C45-1400AC AC 1400W good good n.a.
Power supplies needed by system : 1
Power supplies currently available : 2
Chassis Type : WS-C4507R-E
08-06-2018 01:39 AM
Hello,
what is the output of 'show platform chassis' ?
Check if nothing is obstructing the air flow. If possible, reseat whatever module is inserted in slot 3.
08-06-2018 01:47 AM