Troubleshoot FOr manual ip binding in DHCP
srikanth ath
Level 4
Level 4
hI   experts
WE AHVE cISCO 2960 SWITCHES. this switch acts as a dhcp server for the hosts connected to it.
provided mac based binding to the hosts, with enabled dhcp snooping and IP source guard per interface.'
****i have a problem with single host couldnt get an ip from dhcp as he binded based on mac: manualip****
Here is my config:
we have a VLAN99, 70 hosts connected should get an ip based on mac
switch(2960<config>interface vlan99
# ip address 10.10.14.2 255.255.255.0
#ip dhcp snooping
#ip dhcp snooping vlan 99    ********
# ip dhcp excluded-address 10.10.14.3 10.10.14.10
#ip dhcp excluded-address 10.10.14.80 10.10.14.255
Parent pool
#ip dhcp pool prod
#network 10.10.14.0 255.255.255.0            ********
CHILD pool(sample example for single host bind based on mac-id)
#ip dhcp pool amit
#host 10.10.14.31 255.255.255.0
client-identifier 0101.a0b5.55ea.fb    *******
client-name amit
like this i have i have 70 pools for 70 hosts.
#int fa 0/1-48 (all ports are switch ports of vlan with IPsource guard enabled)
#switchport mode access
#switchport access vlan 99
#ip verify source port-security   *********
the above host amit (10.10.14.31 swhould get this ip bindded with mac) but hez not getting manual ip i.e 10.10.14.31, but if an ip excluded from the dhcp free, he can get that ip i.e automatic ip . every other host are getting the ips as binded in the pool manual ip.
checked with
**sh mac-address table dynamic vlan 99   ()
**clear ip dhcp binding *   or  10.10.14.31
** clear ip dhcp snooping binding
*** clear ip dhcp conflict *
tried to change pool names
all these troubleshoot couldnt make me successs in providing amit an manual ip.
can any1 please tell me whats the main root cause of this prob. as every other hosts could get an manual ip except host called amit as above stated
Requesting a quick reply
thanks
& regards
sreekanth
10 Replies 10
eduardopozo56
Did you check the mac address? Sometimes for some weird reason, the mac address labeled on the NIC or due to NIC changes, you could be using an incorrect mac.
How to check if you are using the correct mac? (The one the DHCP gets)
Just get your host to take a normal Pool address, with no mac binding, a dynamic address, then go to the switch and use the command "show ip dhcp binding", look for the dynamic configured address and You will have the CORRECT mac address there
Then use THAT one as the client identifier
(You will have to clear ip dhcp binding x.x.x.x <- the dynamic ip, or you should get a binding error)
cadet alain
client-identifier 0101.a0b5.55ea.fb  this can't be a valid source MAC address as the I/G is set to 1 which means it is a group address which can only be used as destination.
Regards.
Alain
HI all
please give few mins in going through the attached file.
the mac address i have provided above  is not the correct one.
here is the modifications i have done in assigning ips to hosts. and provided u all the possible outputs in attached file.
10.10.14.39         0110.78d2.c392.df    this is amits mac id..manual binding
10.10.14.93         1078.d2c3.92df          Apr 13 1993 11:14 PM    Automatic  getting automatic ip
if i dint left any ip freee ..amit couldnt get ip from dhcp pool.as so hez not in the network.
can you please look in to the outputs and guide me what should be done.
#sh run
#sh ip dhcp binding
#sh ip dhcp snooping binding
thganks & regards
srikanth
Clear this binding and then change your manual binding like this:
ip dhcp pool amit
hardware-address  01a0.b555.eafb
client-name amit
Regards.
Alain
Hi cadet
whats the difference in using betweeen client-identifier and hardware-adress for child pool..
note: to add on this ,amit is the only one using linux OS. wherein all others are using windows machine does  this may be concern  we need to think about.
Thanks &  regards
srikanth
As you see in the output of sh ip dhcp bindings , the client is using its hardware address  as client-identifier as all Linux do.
So do the change I suggested and your client will get its IP address.
Don't forget to rate posts if helpful.
Regards.
Alain
HI alain
still the same problem persist..
still he got the ip 10.10.14.93 where in he should get 10.10.14.39 (assigned new 1)..
even i saw. the port learned mac-address and its the same mac id which has taken automatic binding.
10.10.14.93         1078.d2c3.92df          Apr 14 1993 03:47 AM    Automatic
is there any thing  sh command i should provide u.
Thanks & regards
srikanth
ip dhcp pool amit
   host 10.10.14.39 255.255.255.0
   hardware-address 0110.78d2.c392.df  --->this is not a valid MAC address
   client-name amit
You didn't clear the binding ?
1078.d2c3.92df   is the correct hardware-address
clear all the  bindings   and  put the correct MAC address
Don't forget to rate if helpful
Regards.
Alain
Hi cadet yes made a mistake in giving correct mac-id...but issue isnt resolved at. will re check the issue. and
rated as you see each and every point  in depth in analysing it and explain us where we are doing mistake
here is the mac id
  1078.d2c3.92df
thanks for your help
will update in short while whether hez getting desired IP. it takes few mins.
regards
srikanth
what you must do is
1) clear the bindings for this MAC address
2) do a dynamic binding to get sure it is using MAC address as client-id
3) reclear the binding fo this client
4) put the correct syntax hardware-address xxxx.xxxx.xxxx
5) renew the lease on the client
Let us know
Regards.
Alain.