11-12-2012 11:41 PM - edited 03-01-2019 10:43 AM
Please Help
UCSM : 1.4 (3l)
Storage FC Ports : fc2/1, fc2/3, fc2/5
error : fc2/5
B(nxos)# sh interface fc 2/5
fc2/5 is down (Link failure: NOS received)
----------------------------------------------------------------------------------------------------------------------
from UCSM
fc port 5 on fabric interconnect B oper state:failed, reason:Link failure: NOS received
-----------------------------------------------------------------------------------------------------------------------
disable and enable port
error : fc2/5
B(nxos)# sh interface fc 2/5
fc2/5 is down (Link failure or not-connected)
wahtis the root cause problem?
Best regards
Solved! Go to Solution.
11-13-2012 02:11 AM
Hello,
NOS refers to "No operatioal sequence". Fibre channel has primitive seqences which are used to establish and maintain a link among the devices.
During the initial login phase,
1.Fiber channel switch sends a NOS signal
2.HBA connected to it sends an "OLS (offline sequence) signal.
3.Switch would send a "Link reset"(LR)
4.HBA responds with a "LRR (link reset response)"
When a NOS received condition is met,
•
A signal loss or sync loss condition is detected.
•
The port is administratively shut down.
•
The port is operationally down.
When the port status is in "link failure or not-connected" state, it means that the physical path is not completely active or no active signals has been sent. Check the cables/SFP's if pluged in properly and check the configuration (port type, speed and vsan settings) for further troubleshooting.
11-13-2012 02:11 AM
Hello,
NOS refers to "No operatioal sequence". Fibre channel has primitive seqences which are used to establish and maintain a link among the devices.
During the initial login phase,
1.Fiber channel switch sends a NOS signal
2.HBA connected to it sends an "OLS (offline sequence) signal.
3.Switch would send a "Link reset"(LR)
4.HBA responds with a "LRR (link reset response)"
When a NOS received condition is met,
•
A signal loss or sync loss condition is detected.
•
The port is administratively shut down.
•
The port is operationally down.
When the port status is in "link failure or not-connected" state, it means that the physical path is not completely active or no active signals has been sent. Check the cables/SFP's if pluged in properly and check the configuration (port type, speed and vsan settings) for further troubleshooting.
11-13-2012 04:52 AM
Hello Pragna,
Thank u so much,
change the cable : solved