lindawa
Introduction
This document describes the steps to setup and configure ACI multi-site fabric from the scratch.
The ACI Multi-Site feature introduced in version 3.0 allows you to interconnect separate Cisco ACI Application Policy Infrastructure Controller (APIC) cluster domains (fabrics), each site that represents a different availability zone. This helps ensure multi-tenant Layer 2 and Layer 3 network connectivity across sites, and it also extends the policy domain end-to-end across fabrics. You can create policies in the Multi-Site GUI and push them to all integrated sites or selected sites. Alternatively, you can import tenants and their policies from a single site and deploy them on other sites.
Contributed by Linda Wang, Cisco TAC Engineer
Prerequisites
Requirements
 1. Setup MultiSite Controller (MSC) by following the Cisco ACI Multi-Site Installation Guide below.
https://www.cisco.com/c/en/us/td/docs/switches/datacenter/aci/aci_multi-site/sw/1x/installation/b_Cisco_ACI_Multi-Site_Installation_Guide/b_Cisco_ACI_Multi-Site_Installation_Guide_chapter_010.html
 2.  ACI fabrics have been fully discovered in two or more sites.
 3. Make sure the APIC clusters deployed in separte sites have the Out of Band (OOB) management connectivity to the MSC nodes.
Components Used
The hardware and software used in this example configuration is listed in the table.
Site A
Hardware Device Logical Name
N9K-C9504 w/ N9K-X9732C-EX spine109
N9K-C93180YC-EX leaf101
N9K-C93180YC-EX leaf102
N9K-C9372PX-E leaf103
APIC-SERVER-M2 apic1
Site B
N9K-C9504 w/ N9K-X9732C-EX spine209
N9K-C93180YC-EX leaf201
N9K-C93180YC-EX leaf202
N9K-C9372PX-E leaf203
APIC-SERVER-M2 apic2
IP Network(IPN) N9K-C93180YC-EX
Hardware     Version
APIC Version 3.1(2m)
MSC
IPN NXOS: version 7.0(3)I4(8a)
Note: The Cross-site namespace normalization is performed by the connecting spine switches, this would require the 2nd generation or newer Cisco Nexus 9000 Series switches with "EX" or "FX" on the end of the product name. Alternatively Nexus 9364C is supported in 1.1(x) and later ACI Multi-Site release.
For more details on hardware requirements and compatibility information, refer to ACI Multi-Site Hardware Requirements Guide .
Configure:
Logical network diagram
Configurations:
This document mainly focuses on ACI and MSC side configuration for Multi-Site deployment and the IPN switch configuration details are not fully covered.  However, a few important configurations from IPN switch are listed below for reference purpose.
IPN Switch configuration
The following are the configuration used in the IPN device connected to the ACI Spines.
vrf context intersite
  description VRF for Multi-Site lab
feature ospf
router ospf intersite
vrf intersite
//Towards to Spine109 in Site-A
// Towards to Spine209 in Site-B
interface Ethernet1/49
  speed 100000
  mtu 9216
  no negotiate auto
  no shutdown
interface Ethernet1/49.4
  mtu 9150
  encapsulation dot1q 4
  vrf member intersite
  ip address 172.16.1.34/27
  ip ospf network point-to-point
  ip router ospf intersite area 0.0.0.1
  no shutdown
interface Ethernet1/50
  speed 100000
  mtu 9216
  no negotiate auto
  no shutdown
interface Ethernet1/50.4
  mtu 9150
  ip address 172.16.2.34/27
  no shutdown
Spoiler
Note: MTU of MP-BGP EVPN control-plane communication between spine nodes in different sites: By default, the spine nodes generate 9000-byte packets for exchanging endpoint routing information. If that default value is not modified, the ISN must support an MTU size of at least 9100 bytes. The default value can be tuned by modifying the corresponding system settings in each APIC domain.
In this example, we are using the default Control Plane MTU size (9000 bytes) on the Spine nodes.
Required configuration from APIC
Step 1: Configure iBGP AS and Route Reflector for each site from APIC GUI
 1. Login the site's APIC and configure iBGP AS and Route Reflector for each site's APIC cluster ( APIC GUI--> System --> System Settings --> BGP Route Reflector) , this is the default BGP Route Route Reflector Policy which will be used for the fabric pod profile.
2. Configure the Fabric POD Profile for each Site's APIC cluster, Go to APIC GUI--> Fabric --> Fabric Policies --> Pod Policies --> Policy Groups, click on the default Pod policy group, select the default "BGP Route Reflector Policy" from the dropdown list, shown as blow.
Step 2: Configure Spine Access Policies include External Routed Domains for each site from APIC GUI
Configure the Spine access policies for Spine uplink to IPN switch with an AEP(Access Entity Profile) and L3 routed domainAPIC GUI--> Fabric --> Access Policies), this part configuration steps will be omitted here, providing with the screenshots for reference.
1) create the switch profile
2) create the AAEP (Attachable Access Entity Profile), Layer 3 Routed domain and VLAN Pool under access policies, shown as below.
3) create the Spine access port policy Group, here associate the Attached Entity Profile "msite".
4) create the spine interface profile, associate the IPN facing spine access port to the interface policy group created in previous step.
Notes:  As for now, there is no need to configure L3Out of OSPF under infra tenant from APIC GUI. We will configure this part via MSC and push the configuration to each site directly later on.
 Step 3: Configure the External Dataplane TEP per site from APIC GUI
Go to APIC GUI--> Infra --> Policies --> Protocol --> Fabric Ext Connection Policies, then create an Intrasite/Intersite Profile, see screenshot below.
Repeat the above steps to complete APIC side configuration for SiteB ACI fabric.
Multi-Site Controller Configuration
Step 1: Add each site one by one in MSC.
  2. Click on the "ADD SITE" menu in order to register the Sites one by one in MSC, you could also see the cluster status on the top right as highlighted.
  3. Use one of the APIC's ip address and assign one unique site ID for each site. (1-127)   13-MultiSite (2) 2018-09-04 16-04-47.png
Step 2: Configure Infra policies per Site in MSC.
  1. Login to MSC GUI, select "Sites" from the left-hand panel, then click on the "CONFIGURE INFRA" menu as shown in the screenshot below.Sites __ CiscoMS 2018-09-04 18-07-24.png
  2. Configure Fabric Infra General settings:  BGP peer type (full mesh - EBGP /route reflector - IBGP)
  3. Once it's done, select one of the sites from the left panel.  Then you will see site info in the middle, there are three different configuration level by clicking on different area. If you can click on The Site , the Pod or the Spine, It will allow different settings on the config panel (right panel)Sites __ CiscoMS 2018-09-04 18-22-15.png
  4. Once we click on each site on the left panel, the site level configurations(Multi-Site Enable (On), Dataplane Multicast TEP, BGP ASN, BGP Community (e.g. extended:as2-nn4:2:22) , OSPF Area ID, OSPF Area Type (stub prevent tep pool advertising), External Route Domain .etc) will show on the right panel. Here we can configure or modify following.
    • Specify Dataplane Multicast TEP (one lo per site) used for HREP
    • BGP AS (matching AS from the site configured in apic)
    • OSPF area type and area id
    • External Routed Domain
In most cases, the attribute values would have already been retrieved automatically from APIC to MSC.
Sites __ CiscoMS 2018-09-04 18-27-02.png5. Next, let's click on the Pod area and go to the POD level specific policies.
Here we need to specify the Data Plane Unicast TEP, as shown below.
6.  Then click on the Spine area and go to Spine specific infra settings, here we can configure followings (as shown in the screenshot below):
For each interface from spine towards to IPN Switch, set IP address and mask,
BGP peer on (yes),
Control Plane TEP (Router Id),
Spine is Reflector (On)
7. Repeat the steps above for other sites and complete the infra configuration in MSC.
8. Click on the "DEPLOY" button at the top,  and this will push the infra configuration to APICs in both sites.
Verify
Step 1: Verify infra configuration from APIC GUI on each APIC cluster
  • Verify the Intrasite/Intersite Profile was configured under infra tenant on each apic cluster.
  • Verify the infra L3Out (intersite), ospf, bgp was configured on each apic cluster (APIC GUI)
  1. Login the site's APIC and verify the Intrasite/Intersite Profile under Tenant infra> Policies > Protocol > Fabric Ext Connection Policies, the Intersite profile will look like following when site is fully configured/managed by MSC. APIC (10.66.93.16) 2018-09-05 15-53-29.png
  2. Go to APIC GUI --> Tenant Infra --> Networking --> External Routed Networks, here the "intersite" L3Out profile should be created automatically under tenant infra in both sites. APIC (10.66.93.16) 2018-09-05 15-57-04.png
And also, the L3Out logical node and interface profile configuration is correctly set in vlan 4.
 Step 2: Verify OSPF/BGP session from Spine CLI on each APIC cluster
  • Verify OSPF is up on spine and gets routes from IPN (Spine CLI)
  • Verify BGP session is up to remote site (Spine CLI)
Login to Spine CLI, verify the BGP l2vpn evpn and OSPF is up on each spine, and also verify the node-role for BGP is msite-speaker
spine109# show ip ospf neighbors vrf overlay-1
 OSPF Process ID default VRF overlay-1
 Total number of neighbors: 1
 Neighbor ID     Pri State            Up Time  Address         Interface
 172.16.1.34       1 FULL/ -          04:13:07 172.16.1.34     Eth1/32.32
spine109#
spine109# show bgp l2vpn evpn summary vrf overlay-1
BGP summary information for VRF overlay-1, address family L2VPN EVPN
BGP router identifier 172.16.1.3, local AS number 100
BGP table version is 235, L2VPN EVPN config peers 1, capable peers 1
0 network entries and 0 paths using 0 bytes of memory
BGP attribute entries [0/0], BGP AS path entries [0/0]
BGP community entries [0/0], BGP clusterlist entries [0/0]
Neighbor V AS MsgRcvd MsgSent TblVer InQ OutQ Up/Down State/PfxRcd
172.16.2.3 4 200 259 259 235 0 0 04:15:39 0
spine109#
spine109# vsh -c 'show bgp internal node-role'
Node role : : MSITE_SPEAKER
spine209# show ip ospf neighbors vrf overlay-1
 172.16.1.34       1 FULL/ -          04:20:36 172.16.2.34     Eth1/32.32
spine209#
spine209# show bgp l2vpn evpn summary vrf overlay-1
BGP router identifier 172.16.2.3, local AS number 200
BGP table version is 270, L2VPN EVPN config peers 1, capable peers 1
172.16.1.3      4   100     264     264      270    0    0 04:20:40 0
spine209#
spine209# vsh -c 'show bgp internal node-role'
Login to Spine CLI to check and verify Overlay-1 interfaces.
ETEP (Multipod Dataplane TEP)
The Dataplane Tunnel Endpoint address used to route traffic between multiple Pods within the single ACI fabric.
DCI-UCAST (Intersite Dataplane unicast ETEP (anycast per site)
This anycast dataplane ETEP address is unique per site, it's assigned to all the spines connected to the IPN/ISN device and used to receive L2/L3 unicast traffic.
DCI-MCAST-HREP (Intersite Dataplane multicast TEP)
This anycast ETEP address is assigned to all the spines connected to the IPN/ISN device and used to receive L2 BUM (Broadcast, Unknown unicast and Multicast) traffic.
MSCP-ETEP (Multi-Site Control-plane ETEP)
This is the control plane ETEP address, which is also known as BGP Router ID on each spine for MP-BGP EVPN.
spine109# show ip int vrf overlay-1
<snip>
lo17, Interface status: protocol-up/link-up/admin-up, iod: 83, mode: etep
  IP address: 172.16.1.4, IP subnet: 172.16.1.4/32
  IP broadcast address: 255.255.255.255
  IP primary address route-preference: 1, tag: 0
lo18, Interface status: protocol-up/link-up/admin-up, iod: 84, mode: dci-ucast
  IP address: 172.16.1.1, IP subnet: 172.16.1.1/32
lo19, Interface status: protocol-up/link-up/admin-up, iod: 85, mode: dci-mcast-hrep
  IP address: 172.16.1.2, IP subnet: 172.16.1.2/32
lo20, Interface status: protocol-up/link-up/admin-up, iod: 87, mode: mscp-etep
  IP address: 172.16.1.3, IP subnet: 172.16.1.3/32
spine209# show ip int vrf overlay-1
<snip>
lo13, Interface status: protocol-up/link-up/admin-up, iod: 83, mode: etep
  IP address: 172.16.2.4, IP subnet: 172.16.2.4/32
lo14, Interface status: protocol-up/link-up/admin-up, iod: 84, mode: dci-ucast
  IP address: 172.16.2.1, IP subnet: 172.16.2.1/32
lo15, Interface status: protocol-up/link-up/admin-up, iod: 85, mode: dci-mcast-hrep
  IP address: 172.16.2.2, IP subnet: 172.16.2.2/32
lo16, Interface status: protocol-up/link-up/admin-up, iod: 87, mode: mscp-etep
  IP address: 172.16.2.3, IP subnet: 172.16.2.3/32
At the end, Make sure no faults is seen from MSC (multi-site controller)
 Reference
   Cisco ACI Multi-Site Architecture White Paper
Dan Verzaal
Level 4
Level 4
Very helpful document for Multisite!
Keep them coming :)
Shangxin Du
Thank you for putting this together, it was really helpful!
Siemmina
Amazing!!
I was looking for more information about the requirements of the Intersite network:
- what are the supported interconnection technologies that used connect the mutli-site: the white paper was showing Dark fiber from 10G to 100GB, ...is it possible to use MPLS with a bandwidth of 500 MB
- Which kind of switched L3 could be used as an IPN switch? is it enough an Switch Layer 3 or it needs an ASR?
Thank you for the post and your help.
nkhawaja1
This is a great document, but it needs to be updated now for version 4.2, please add remote L3out configuration and Verification Scenario as well.
lindawa
Hi @Siemmina
Thanks for your message.
The answers to your questions are documented in the white paper, as quoted below.
Q1: what are the supported interconnection technologies that used connect the mutli-site In terms of bandwidth?
"The recommended connection bandwidth between nodes in a Cisco ACI Multi-Site Orchestrator cluster is from 300 Mbps to 1 Gbps. These numbers are based on internal stress testing while adding very large configurations and deleting them at high frequency. In these tests, bursts of traffic of up to 250 Mbps were observed during high-scale configurations, and bursts of up to 500 Mbps were observed during deletion of a configuration consisting of 10,000 EPGs (that is, beyond the supported scale of 3000 EPGs for Cisco ACI Multi-Site deployments in Cisco ACI Release 3.2(1)). "
Q2: - Which kind of switched L3 could be used as an IPN switch? is it enough an Switch Layer 3 or it needs an ASR?
A2: The Inter-Site Network (ISN) is instead a simpler routed infrastructure required to interconnect the different fabrics (only requiring support for increased MTU). So it doesn't need to be an ASR.
Hope it helps,
Cheers,
Linda
lindawa
Thanks for your comments, @nkhawaja1
This document explains the steps to setup and configure ACI multi-site fabric from the scratch, it also applies to later release of MSO, remote L3out configuration and Verification Scenario can be a separated document.
Cheers,
Linda
muarain
Hi Linda,
Great and very helpful document especially the verification portion.
Thanks for help
Sajid Arain
rodrigo-freitas
Hi Linda.
Thank you very much for share this document. Really very helpful.
I've a doubt about WAN connection.  When I've a cenario with ISN connected a CPE router, the interface must to be associated to vrf and the SP must be vrf end-to-end toward other site right?
There is any problem in configure it out of vrf?
I ask this because I've a customer that haven't MPLS on WAN link.
Best Regards,
Rod.
Helpful Document
bijupadmanabh
Hi @lindawa
I would like to know the Minimum Bandwidth Requirement that we need to plan for the Site to Site Connectivity - in case of Cisco Multisite - Active / Active  DC. Considering VLAN STRETCHING between the site. Please consider the Site to site Fabric connectivity requirement as well as production data flow ( infra traffic ).
Thanks & regards