cisco nexus 7000 compatibility

junhyeok89
Level 1
Level 1

I totally wonder below a compatibility of the Nexus 7000 modules

I have not found something related that

 

Can this hardware compatibility be OK?

Q1) SUP2 + Fabric module 1

Q2) SUP2E + Fabric module 1

Q3) SUP1 + Fabric module 2

Q4) Fabric module 1 + Fabric module 2

 

3 Replies 3

Hello and good morning--could you kindly clarify your question?  What sort of fabric are you talking about? 

 

Thank you, MM

thank you for your response

fabric is fabric module 

 

thank you :)

Souvik Ghosh
Cisco Employee
Cisco Employee

Hi,

yes for 1,2 and 3. Difference will be in backplane speed.

for 4. it is not recommended to mix fab1 with fab2. if you mix fab1 and fab2 following will happen:

 

https://www.cisco.com/c/en/us/td/docs/switches/datacenter/hw/nexus7000/installation/guide/n7k_hig_book/n7k_managing_sys_hw.html#wp1052265

 

Note You can replace a Fabric 1 module with a Fabric 2 module in the Cisco Nexus 7010 and 7018 switches during operations, but while there is a mix of fabric module types, all of the fabric modules perform as Fabric 1 modules. If you power up a switch with both types of fabric modules installed, only the Fabric 2 modules will power up. To utilize the Fabric 2 module capabilities, all of the installed fabric modules must be Fabric 2 modules.

 

thanks

souvik

 

 

 