Bookmark
Subscribe
6305
IP SLA not working
lucap
I have a problem with IP SLA.
The conf seems ok and I have no error.
But values are 0 except for RTT.
gw1#sh ip sla stat
Round Trip Time (RTT) for       Index 1
Type of operation: jitter
        Latest RTT: 18 ms
Latest operation start time: 22:25:29.597 MDT Fri Oct 20 2017
Latest operation return code: OK
RTT Values
        Number Of RTT: 10
        RTT Min/Avg/Max: 17/18/20 ms
Latency one-way time milliseconds
        Number of Latency one-way Samples: 0
        Source to Destination Latency one way Min/Avg/Max: 0/0/0 ms
        Destination to Source Latency one way Min/Avg/Max: 0/0/0 ms
Jitter time milliseconds
        Number of SD Jitter Samples: 0
        Number of DS Jitter Samples: 0
        Source to Destination Jitter Min/Avg/Max: 0/0/0 ms
        Destination to Source Jitter Min/Avg/Max: 0/0/0 ms
Packet Loss Values
        Loss Source to Destination: 0           Loss Destination to Source: 0
        Out Of Sequence: 0      Tail Drop: 10
        Packet Late Arrival: 0  Packet Skipped: 0
Voice Score Values
        Calculated Planning Impairment Factor (ICPIF): 0
        Mean Opinion Score (MOS): 0
Number of successes: 23
Number of failures: 0
Operation time to live: Forever
The responder has no error too:
gw2#sh ip sla resp
        General IP SLA Responder on Control port 1967
        General IP SLA Responder on Control V2 port 1167
General IP SLA Responder is: Enabled
Number of control message received: 165 Number of errors: 0
Recent sources:
        10.1.1.1 [22:27:44.588 MDT Fri Oct 20 2017]
        10.1.1.1 [22:27:29.588 MDT Fri Oct 20 2017]
        10.1.1.1 [22:27:14.592 MDT Fri Oct 20 2017]
        10.1.1.1 [22:26:59.580 MDT Fri Oct 20 2017]
        10.1.1.1 [22:26:44.584 MDT Fri Oct 20 2017]
Recent error sources:
Number of control v2 message received: 0 Number of errors: 0
Recent sources:
        Permanent Port IP SLA Responder
Permanent Port IP SLA Responder is: Enabled
udpEcho Responder:
  IP Address             Port
  10.2.2.2          65501
Conf is very simple:
ip sla 1
 udp-jitter 10.2.2.2 65501 source-ip 10.1.1.1
 frequency 15
ip sla schedule 1 life forever start-time now
ip sla enable reaction-alerts
Any help is very appreciated. Thanks
My bad, that was in your first post already.
Either way, how are the devices connected ? I did this in GNS3 with back to back routers, the only thing I left out on the responder was the line:
ip sla responder udp-echo ipaddress 10.2.2.2 port 65501
Can you try that, take out that line ?
6 Replies 6
Hello @lucap
 You need to have the same Time synchronization between both ends.
Check this out.
-If I helped you somehow, please, rate it as useful.-
Hello
Yes, both routers are synchronized with the same time server
gw1#sh ntp s
Clock is synchronized, stratum 2, reference is 193.204.114.233
nominal freq is 119.2092 Hz, actual freq is 119.2081 Hz, precision is 2**18
reference time is DD958BD6.EB827E74 (11:03:18.919 MDT Sat Oct 21 2017)
clock offset is 0.4451 msec, root delay is 5.05 msec
root dispersion is 1.48 msec, peer dispersion is 0.75 msec
gw2#sh ntp s
Clock is synchronized, stratum 2, reference is 193.204.114.232
nominal freq is 250.0000 Hz, actual freq is 249.9993 Hz, precision is 2**21
ntp uptime is 3456787300 (1/100 of seconds), resolution is 4016
reference time is DD958C71.F921101D (11:05:53.973 MDT Sat Oct 21 2017)
clock offset is 0.6327 msec, root delay is 15.44 msec
root dispersion is 7.04 msec, peer dispersion is 0.11 msec
loopfilter state is 'CTRL' (Normal Controlled Loop), drift is 0.000002725 s/s
system poll interval is 512, last update was 407 sec ago.
Thank you
enable the 'ip sla responder' globally on the destination device:
Router(config)#ip sla responder
It's already enabled
gw2#sh run | i sla
ip sla responder
gw2#sh ip sla resp
Number of control message received: 8882 Number of errors: 0
Recent sources:
        10.1.1.1 [10:47:00.813 MDT Sun Oct 22 2017]
        10.1.1.1 [10:46:45.813 MDT Sun Oct 22 2017]
        10.1.1.1 [10:46:30.813 MDT Sun Oct 22 2017]
        10.1.1.1 [10:46:15.817 MDT Sun Oct 22 2017]
        10.1.1.1 [10:46:00.817 MDT Sun Oct 22 2017]
Recent sources:
udpEcho Responder:
  IP Address             Port
  10.2.2.2          65501
Thank you
It works!
Just to note I put that line in the conf following the guide:
https://www.cisco.com/c/en/us/td/docs/switches/lan/catalyst3750/software/release/12-2_55_se/configuration/guide/scg3750/swipsla.html
Thank you very much!