Hello. So in my small business we have an sg350-28. It has been great.
The problem is, currently it is on a UPS that has a 8ms time between ac loss to switching over to battery.
So we have a new UPS that has a 16.6ms switch over time. All the other devices we have are fine with this. However I cannot find the specs on the sg350-28 power supply.
Dose anyone know what the hold up time is?
06-03-2021 03:35 PM
as i remember 10 years or more testing with APC UPS , Online UPS vs Line Interactive UPS. it was 10ms hold time device can able to co-up, before the power not served the device reboots.
this may be changed, never got any chance to test, since most new world has dual feeds online UPS.
06-03-2021 06:11 PM
10 is pretty low. ATX standard is 17. Industrial equipment is 50.
I really hope its not 10. It would be the only thing in the rack that is that short.
I just tested a 15 year old SMC 24 port 10/100 switch and it did the 16.6 fine 3 times back to back.
I will keep you updated on the situation. Worst case scenario the switch will have to have its own UPS.
06-04-2021 02:46 AM
The Hold-up time of the SG350 series PSUs is greater than 10ms. Hold-up time is measured when the AC line is shut off to the drop of the 12V DC output goes below 10.8V with a full load and no external output capacitor.
Thanks,
Martin
06-04-2021 04:49 AM
sure that was my test case, it may be changed in the new era as mentioned. test and advise.