11-26-2012 09:28 AM - edited 03-07-2019 10:15 AM
I have a minor alarm about the clock on a 6509. Does this mean it needs to be replaced or is it in some kind of standby status?
Here are my two alarms about the clock modules,
Port-Mariners#show environment alarm
environmental alarms:
system minor alarm on operating clock count (raised 21w0d ago)
system minor alarm on clock 2 OK (raised 21w0d ago)
The module doesn't say Fail or anything like I've seen in other user posted output. For example,
########
https://supportforums.cisco.com/message/546682#546682
sh env
Environmental Status (. = Pass, F = Fail, U = Unknown, N = Not Present)
PS1: . PS2: . PS1 Fan: . PS2 Fan: .
Chassis-Ser-EEPROM: . Fan: .
Clock(A/B): A Clock A: . Clock B: F
VTT1: . VTT2: . VTT3: .
##############
I've read as much as I could find about the clock module but nothing to tell me if it definitely needs to be replaced or is still usable.
http://docwiki.cisco.com/wiki/Replace_CLK-7600_WS-C6509-V-E
Here is the complete output from sh environment,
#sh environment
environmental alarms:
system minor alarm on operating clock count (raised 21w0d ago)
system minor alarm on clock 2 OK (raised 21w0d ago)
backplane:
operating clock count: 1
operating VTT count: 3
fan-tray 1:
fan-tray 1 type: WS-C6K-9SLOT-FAN2
fan-tray 1 version: 2
fan-tray 1 fan-fail: OK
VTT 1:
VTT 1 OK: OK
VTT 1 outlet temperature: 33C
VTT 2:
VTT 2 OK: OK
VTT 2 outlet temperature: 33C
VTT 3:
VTT 3 OK: OK
VTT 3 outlet temperature: 48C
clock 1:
clock 1 OK: OK, clock 1 clock-inuse: in-use
clock 2:
clock 2 OK: not OK, clock 2 clock-inuse: not-in-use
power-supply 1:
power-supply 1 fan-fail: OK
power-supply 1 power-input: AC high
power-supply 1 power-output-mode: high
power-supply 1 power-output-fail: OK
power-supply 2:
power-supply 2 fan-fail: OK
power-supply 2 power-input: AC high
power-supply 2 power-output-mode: high
power-supply 2 power-output-fail: OK
module 1:
module 1 power-output-fail: OK
module 1 outlet temperature: 34C
module 1 inlet temperature: 29C
module 1 device-1 temperature: 37C
module 1 device-2 temperature: 31C
module 1 VDB outlet temperature: 34C
module 1 VDB inlet temperature: 33C
module 1 VDB device-1 temperature: 32C
module 2:
module 2 power-output-fail: OK
module 2 outlet temperature: 30C
module 2 inlet temperature: 29C
module 2 device-1 temperature: 29C
module 2 device-2 temperature: 30C
module 3:
module 3 power-output-fail: OK
module 3 outlet temperature: 31C
module 3 inlet temperature: 29C
module 3 device-1 temperature: 29C
module 3 device-2 temperature: 33C
module 4:
module 4 power-output-fail: OK
module 4 outlet temperature: 29C
module 4 inlet temperature: 26C
module 6:
module 6 power-output-fail: OK
module 6 outlet temperature: 35C
module 6 inlet temperature: 29C
module 6 device-1 temperature: 39C
module 6 device-2 temperature: 39C
module 6 asic-1 (SSO-1) temp: 29C
module 6 asic-2 (SSO-2) temp: 28C
module 6 asic-3 (SSO-3) temp: 28C
module 6 asic-4 (SSO-4) temp: 28C
module 6 asic-5 (SSA-1) temp: 28C
module 6 asic-6 (HYPERION-1) temp: 29C
module 6 RP outlet temperature: 29C
module 6 RP inlet temperature: 29C
module 6 EARL outlet temperature: 44C
module 6 EARL inlet temperature: 27C
chassis connector rating: 1260.00 Watts (30.00 Amps @ 42V)
module 1
module 1 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
module 1 vdb connector rating: 850.08 Watts (20.24 Amps @ 42V)
module 1 power consumption: 53.76 Watts ( 1.28 Amps @ 42V)
module 2
module 2 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
module 2 power consumption: 103.74 Watts ( 2.47 Amps @ 42V)
module 3
module 3 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
module 3 power consumption: 103.74 Watts ( 2.47 Amps @ 42V)
module 4
module 4 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
module 4 power consumption: 84.00 Watts ( 2.00 Amps @ 42V)
module 6
module 6 connector rating: 1260.00 Watts (30.00 Amps @ 42V)
module 6 power consumption: 315.00 Watts ( 7.50 Amps @ 42V)
chassis per slot cooling capacity: 70 cfm
ambient temperature: < 55C
module 1 cooling requirement: 30 cfm
module 2 cooling requirement: 30 cfm
module 3 cooling requirement: 30 cfm
module 4 cooling requirement: 30 cfm
module 6 cooling requirement: 35 cfm
12-29-2012 12:41 PM
Ended up just replacing the clock module hardware. Now my status shows both clocks as working.