C6509 Power input - question

Yannick Vranckx
Level 2
Level 2

Hello,

We have a 6509 chassis with 2 supervisors, this chassis also has 2 power supplies installed.

Now i have noticed that 1 of the 2 power supplies seems to not be supplying the full power it should.

So for example the output is showing:

Power-Capacity PS-Fan Output Oper PS Type Watts A @42V Status Status State ---- ------------------ ------- ------ ------ ------ ----- 1 WS-CAC-6000W 5771.64 137.42 OK OK on SSEC2-IFPU2#sh power status power-supply 2 Power-Capacity PS-Fan Output Oper PS Type Watts A @42V Status Status State ---- ------------------ ------- ------ ------ ------ ----- 2 WS-CAC-6000W 2671.20 63.60 OK OK on It is showing me that PSU is delivering close to 6000W, but the second one is half of its capacity. We have just been informed that the 2 power connectors on the PSU should be connected properly, Is there a way to check this connection? power-supply 1: power-supply 1 fan-fail: OK power-supply 1 power-input: AC high power-supply 1 power-output-mode: high power-supply 1 power-output-fail: OK power-supply 2: power-supply 2 fan-fail: OK power-supply 2 power-input: AC low power-supply 2 power-output-mode: low power-supply 2 power-output-fail: OK Also here i see that on power-supply 2, the power output mode: low. Is this normal or to be expected? Any documentation on this?
3 Replies 3

Carlos Villagran
Cisco Employee
Cisco Employee

Hi Yannick!

Please refer to the Power Supply specifications:

http://www.cisco.com/c/en/us/td/docs/switches/lan/catalyst6500/hardware/Chassis_Installation/Cat6500/6500_ins/0apwsply.html

The 6000 W power supply can operate at either 2900 W or 6000 W depending on the number of AC power cords attached and the source AC voltage.

Note The 6000 W AC-input power supply is limited to 4000 W maximum output when it is installed in a Catalyst 6506, Catalyst 6509, or Catalyst 6509-NEB switch chassis. The power supply is limited to 4500 W maximum output when it is installed in the Catalyst 6509-NEB-A switch chassis.

  • 2900 W maximum with the following source AC arrangements:

INPUT 1 and INPUT 2 both connected to low-line (120 VAC nominal)

INPUT 1 connected to high-line (230 VAC nominal); INPUT 2 not connected

INPUT 1 not connected; INPUT 2 connected to high-line (230 VAC nominal)

INPUT 1 connected to high-line (230 VAC nominal); INPUT 2 connected to low-line (120 VAC nominal)

INPUT 1 connected to low-line (120 VAC nominal); INPUT 2 connected to high-line (230 VAC nominal)

  • 6000 W maximum with the following source AC arrangements:

INPUT 1 and INPUT 2 both connected to high-line (230 VAC nominal)

Please check the requirement for 6000 W operation, be sure that INPUT 1 and 2 in the PSU are connected to a 230VAC power source.

Hope it helps,

JC

Ok,

I love it when Cisco documentation is cryptic.

So it looks there is an issue with the power input from the second power supply? Since the first one is generating 5700W and the second one 2600W.

So in order to use the 6000W mode, both supplies need to be high power mode?

system power redundancy mode = redundant
system power total =     5771.64 Watts (137.42 Amps @ 42V)
system power used =      1630.44 Watts (38.82 Amps @ 42V)
system power available = 4141.20 Watts (98.60 Amps @ 42V)
                        Power-Capacity PS-Fan Output Oper
PS   Type               Watts   A @42V Status Status State
---- ------------------ ------- ------ ------ ------ -----
1    WS-CAC-6000W       5771.64 137.42 OK     OK     on
2    WS-CAC-6000W       2671.20 63.60  OK     OK     on
                        Pwr-Allocated  Oper
Fan  Type               Watts   A @42V State
---- ------------------ ------- ------ -----
1    WS-C6509-E-FAN      150.36  3.58  OK
                        Pwr-Requested  Pwr-Allocated  Admin Oper
Slot Card-Type          Watts   A @42V Watts   A @42V State State
---- ------------------ ------- ------ ------- ------ ----- -----
1    ACE30-MOD-K9        335.16  7.98   335.16  7.98  on    on
2    WS-X6748-SFP        254.94  6.07   254.94  6.07  on    on
3    WS-X6748-GE-TX      325.50  7.75   325.50  7.75  on    on
5    WS-SUP720-3B        282.24  6.72   282.24  6.72  on    on
6    WS-SUP720-3B        282.24  6.72   282.24  6.72  on    on
system auxiliary power mode = off
system auxiliary power redundancy operationally = non-redundant
system primary connector power limit =   10920.00 Watts (260.00 Amps @ 42V)
system auxiliary connector power limit = 10500.00 Watts (250.00 Amps @ 42V)
system primary power used =              1630.44 Watts (38.82 Amps @ 42V)
system auxiliary power used =            0 Watt

It is still showing the power mode as redundant, but you can clearly see that the second power supply is just not giving the same amount of watts. Is this normal behaviour or something?

power-supply 2:
  power-supply 2 fan-fail: OK
  power-supply 2 power-input: AC low
  power-supply 2 power-output-mode: low
  power-supply 2 power-output-fail: OK