Cisco Nexus 7000 ambient and working temperature

ANAKIN_TN
Level 1
Level 1

Hello all,

 

I have two nexus 7009 chassis fully staffed with N7K-F248XP-25 E   modules

 

in the environnemental condition on this link https://www.cisco.com/c/en/us/products/collateral/switches/nexus-7000-series-switches/data_sheet_c78-720322.html

 

Environmental conditions

• Operating temperature: 32 to 104°F (0 to 40°C)

• Storage temperature: -40 to 185°F (-40C to 85°C)

• Relative humidity operating, noncondensing: 10 to 90%

• Relative humidity nonoperating, noncondensing: 10 to 95%

 

the recommanded working temperature are between 0 to 40°  degrees, in  my datacenter temperature is between 20 and 23 ° but whats is shown with the command show env, shows that i have lot of sensors in module showing that the temperture are going beyon 40° so it does mean that my chassis and card are workin in a hot environment ?

the Environmental conditions is the datacenter temperature or the temperature showed by the sensors ?

 

sh env core 1.png

 

Cordialement

 

3 Replies 3

marce1000
VIP
VIP

 

                  >that my chassis and card are working in a hot environment 

  Not necessarily those are internal measurements . If you get no temperature alarms, don't worry.

 M.

 



-- Each morning when I wake up and look into the mirror I always say ' Why am I so brilliant ? '
    When the mirror will then always repond to me with ' The only thing that exceeds your brilliance is your beauty! '

Hi Marce,

 

Sure ? because last year i had many issue with cards temperature sensor or broken ports on the same ASIC .
look to the screenshot, a crossbar of module 4 showing 52° or the L2L3dev3 of module 3 showing 57°

 

Regards

Hello!

I can confirm that these temperatures look nominal. Here is output from my lab, which shows similar temperatures (if not higher in some cases):

switch# show environment temperature | include L2L3|----|Status
--------------------------------------------------------------------
Module   Sensor        MajorThresh   MinorThres   CurTemp     Status
--------------------------------------------------------------------
1        L2L3Dev1(s5)    125             115         50         Ok             
1        L2L3Dev2(s6)    125             115         46         Ok             
1        L2L3Dev3(s7)    125             115         49         Ok             
1        L2L3Dev4(s8)    125             115         48         Ok             
1        L2L3Dev5(s9)    125             115         50         Ok             
1        L2L3Dev6(s10)   125             115         44         Ok             
2        L2L3Dev1Sn1(s8) 125             115         55         Ok             
2        L2L3Dev1Sn2(s9) 125             115         59         Ok             
2        L2L3Dev2Sn1(s12 125             115         52         Ok             
2        L2L3Dev2Sn2(s13 125             115         56         Ok             
3        L2L3Dev1(s3)    125             110         44         Ok             
6        L2L3Dev1Sn1(s8) 125             115         51         Ok             
6        L2L3Dev1Sn2(s9) 125             115         56         Ok             
6        L2L3Dev2Sn1(s12 125             115         49         Ok             
6        L2L3Dev2Sn2(s13 125             115         53         Ok             
6        L2L3Dev3Sn1(s16 125             115         49         Ok             
6        L2L3Dev3Sn2(s17 125             115         52         Ok             
6        L2L3Dev4Sn1(s20 125             115         51         Ok             
6        L2L3Dev4Sn2(s21 125             115         54         Ok 

Thank you!

-Christopher 