05-26-2010 11:19 AM - edited 03-06-2019 11:16 AM
Hello,
I apologize if this is clearly documented somewhere but I was not able to find an answer. I have a couple Nexus 7ks with 6kW PSUs installed and 30a/208v whips under the cabinet. I know the 7.5kW PSUs require 30A circuits and thus ship with the NEMA 6L-30 cord option. What I can't determine is will the 6kW PSUs run on 30A AC circuits and if so will the same NEMA 6L-30 cord designed for the 7.5kW PSUs work on the 6kW PSUs?
Thanks,
-Matt
Solved! Go to Solution.
05-26-2010 11:38 AM
Hello Matt,
6 KW power supplies have different AC inputs and use different cables
see
http://www.cisco.com/en/US/prod/collateral/switches/ps9441/ps9402/ps9512/Data_Sheet_C78-437761.html
6KW
International Electrotechnical Commission (IEC) 320-C19
7,5 KW
IEC 60309 for INT
NEMA L6-30 for US
there are also pictures showing clearly the AC inputs have different shapes
We have recently installed two
here is the sample of sh environment power
sh environment power
Power Supply:
Voltage: 50 Volts
Power Actual Total
Supply Model Output Capacity Status
(Watts ) (Watts )
------- ------------------- ----------- ----------- --------------
1 N7K-AC-6.0KW 512 W 6000 W Ok
2 N7K-AC-6.0KW 469 W 6000 W Ok
3 N7K-AC-6.0KW 579 W 6000 W Ok
Actual Power
Module Model Draw Allocated Status
(Watts ) (Watts )
------- ------------------- ----------- ----------- --------------
1 N7K-M132XP-12 N/A 750 W Powered-Up
5 N7K-SUP1 N/A 210 W Powered-Up
6 N7K-SUP1 N/A 210 W Powered-Up
10 N7K-M132XP-12 N/A 750 W Powered-Up
Xb1 N7K-C7010-FAB-1 N/A 60 W Powered-Up
Xb2 N7K-C7010-FAB-1 N/A 60 W Powered-Up
Xb3 N7K-C7010-FAB-1 N/A 60 W Powered-Up
Xb4 N7K-C7010-FAB-1 N/A 60 W Powered-Up
Xb5 N7K-C7010-FAB-1 N/A 60 W Powered-Up
fan1 N7K-C7010-FAN-S N/A 720 W Powered-Up
fan2 N7K-C7010-FAN-S N/A 720 W Powered-Up
fan3 N7K-C7010-FAN-F N/A 120 W Powered-Up
fan4 N7K-C7010-FAN-F N/A 120 W Powered-Up
N/A - Per module power not available
Power Usage Summary:
--------------------
Power Supply redundancy mode (configured) PS-Redundant
Power Supply redundancy mode (operational) PS-Redundant
Total Power Capacity (based on configured mode) 12000 W
Total Power of all Inputs (cumulative) 18000 W
Total Power Output (actual draw) 1560 W
Total Power Allocated (budget) 3900 W
Total Power Available for additional modules 8100 W
05-26-2010 11:38 AM
Hello Matt,
6 KW power supplies have different AC inputs and use different cables
see
http://www.cisco.com/en/US/prod/collateral/switches/ps9441/ps9402/ps9512/Data_Sheet_C78-437761.html
6KW
International Electrotechnical Commission (IEC) 320-C19
7,5 KW
IEC 60309 for INT
NEMA L6-30 for US
there are also pictures showing clearly the AC inputs have different shapes
We have recently installed two
here is the sample of sh environment power
sh environment power
Power Supply:
Voltage: 50 Volts
Power Actual Total
Supply Model Output Capacity Status
(Watts ) (Watts )
------- ------------------- ----------- ----------- --------------
1 N7K-AC-6.0KW 512 W 6000 W Ok
2 N7K-AC-6.0KW 469 W 6000 W Ok
3 N7K-AC-6.0KW 579 W 6000 W Ok
Actual Power
Module Model Draw Allocated Status
(Watts ) (Watts )
------- ------------------- ----------- ----------- --------------
1 N7K-M132XP-12 N/A 750 W Powered-Up
5 N7K-SUP1 N/A 210 W Powered-Up
6 N7K-SUP1 N/A 210 W Powered-Up
10 N7K-M132XP-12 N/A 750 W Powered-Up
Xb1 N7K-C7010-FAB-1 N/A 60 W Powered-Up
Xb2 N7K-C7010-FAB-1 N/A 60 W Powered-Up
Xb3 N7K-C7010-FAB-1 N/A 60 W Powered-Up
Xb4 N7K-C7010-FAB-1 N/A 60 W Powered-Up
Xb5 N7K-C7010-FAB-1 N/A 60 W Powered-Up
fan1 N7K-C7010-FAN-S N/A 720 W Powered-Up
fan2 N7K-C7010-FAN-S N/A 720 W Powered-Up
fan3 N7K-C7010-FAN-F N/A 120 W Powered-Up
fan4 N7K-C7010-FAN-F N/A 120 W Powered-Up
N/A - Per module power not available
Power Usage Summary:
--------------------
Power Supply redundancy mode (configured) PS-Redundant
Power Supply redundancy mode (operational) PS-Redundant
Total Power Capacity (based on configured mode) 12000 W
Total Power of all Inputs (cumulative) 18000 W
Total Power Output (actual draw) 1560 W
Total Power Allocated (budget) 3900 W
Total Power Available for additional modules 8100 W
05-26-2010 12:49 PM
Giuseppe,
Good point. And it does not appear Cisco makes a power cord for the 6kW PSU with the NEMA 6L-30 plug type on the far end. Thanks for your input.
-Matt
Discover and save your favorite ideas. Come back to expert answers, step-by-step guides, recent topics, and more.
New here? Get started with these tips. How to use Community New member guide