Hi, we have 4507R+E at the distribution layer. Since last 6 months, we are facing a "temperature warnings" in some of our modules including the supervisor modules, the switches are placed at normal room temperature with ACs provided for cooling. Whenever the warning comes, we take out the module, clean it with a blower, and the warning disappears. But after a few days the warning appears again. What could be causing this.
The output of "show environment " of one such switch is attached here for your reference.
What could be the exact reason of this problem.
Thanks
05-07-2015 02:53 AM
Hi,
Pls check the rack air flow direction should be alligned as beow for 4507 R+E
Chassis fan tray: Right to left
Power supply fan: Front to back
Vivek
- See more at: https://supportforums.cisco.com/discussion/12500681/temperature-warning-4507-re#comment-10582486
06-10-2015 05:49 AM
Hi all
could you explain to me what the names here - XPP , NFE , VFE .... - mean ? CPU , AIR in / outlet is already clear .
And which value is to compare with a non- modular Switch ?
In Nagios what value should I take to see the correct Temperature .
Thank you All .
- See more at: https://supportforums.cisco.com/discussion/12500681/temperature-warning-4507-re#comment-10582491