09-19-2013 08:51 AM - edited 03-01-2019 11:15 AM
Folks,
I think PSU2 has failed:
atl01-ucsf01a-A /server # show psu detail
PSU:
PSU: 1
Overall Status: Operable
Operability: Operable
Threshold Status: OK
Power State: On
Presence: Equipped
Thermal Status: OK
Voltage Status: OK
Product Name: 650W power supply, with added 5A Standby for UCS C200 or C210
PID: R2X0-PSU2-650W-SB
VID: V00
Vendor: Cisco Systems Inc
Serial (SN): QCI15411SCZ
HW Revision: 0
PSU: 2
Overall Status: N/A
Operability: N/A
Threshold Status: N/A
Power State: PwrSave
Presence: Equipped
Thermal Status: OK
Voltage Status: N/A
Product Name: 650W power supply, with added 5A Standby for UCS C200 or C210
PID: R2X0-PSU2-650W-SB
VID: V00
Vendor: Cisco Systems Inc
Serial (SN): QCI15391R9C
HW Revision: 0
However, UCS isn't showing a fault:
atl01-ucsf01a-A /server # show fault
atl01-ucsf01a-A /server #
Any assistance is appreciated.
Cheers,
Paul
Solved! Go to Solution.
09-22-2013 11:52 PM
Hello Paul,
I would request you to open a TAC SR with UCSM and rack server techsupport to further investigate this issue.
Padma
09-19-2013 09:18 AM
Hello Paul,
Looks like UCSM managed rack server ( C210 M2 ) . The second PSU of the rack server is in power save mode and it is NOT faulty hardware state.
What is the power policy configured in UCSM ?
UCSM version ?
Padma
09-19-2013 11:21 AM
Hello,
It is indeed a UCSM managed C210 M2:
atl01-ucsf01a-A /server # show inventory
Server 11:
Name: ATL-L09-U24
Acknowledged Serial (SN): QCI1543AD3U
Acknowledged Product Name: Cisco UCS C210 M2
Acknowledged PID: R210-2121605W
Acknowledged VID: 0
Acknowledged Memory (MB): 98304
Acknowledged Effective Memory (MB): 98304
Acknowledged Cores: 8
Acknowledged Adapters: 1
Here's the rest of the information you were looking for:
atl01-ucsf01a-A# show version
System version: 2.0(3c)
atl01-ucsf01a-A# scope org
atl01-ucsf01a-A /org # show psu-policy
PSU Policy:
Redundancy Description
---------- -----------
Grid
I think this is the power policy information you were looking for?
Cheers,
Paul
09-21-2013 08:54 AM
Hello Paul,
Do you have any other server with above behavior ?
I need to read whether Grid power policy configuration will push the second PSU into standy mode or not.
Padma
09-21-2013 09:52 AM
Padma,
This is the only server with the above behavior. I've power cycled the server, and also reacknowledged it, but the PSU remains in the same state.
Cheers,
Paul
09-22-2013 11:52 PM
Hello Paul,
I would request you to open a TAC SR with UCSM and rack server techsupport to further investigate this issue.
Padma
09-30-2013 10:51 AM
Opened case with TAC, and replacing the power supply resolved the issue.
09-30-2013 10:25 PM
Thanks for sharing the solution.
Discover and save your favorite ideas. Come back to expert answers, step-by-step guides, recent topics, and more.
New here? Get started with these tips. How to use Community New member guide