cancel
Showing results for 
Search instead for 
Did you mean: 
cancel
347
Views
0
Helpful
1
Replies

Cisco Aironet Lightning Arrestor

FabArcSteel
Level 1
Level 1

I know that 0 ohms is a dream when dealing with grounding rods, but what maximum ohms will fit within tolerance of the AIR-ACC245LA-R Arrestor?

For better clarification, what is the maximun tolerable resistance of the grounding rod necessary to make the arrestor able to do its job?

1 Reply 1

didyap
Level 6
Level 6

For the grounding rod, resistance should be as much as possible low. you have to take care of this two points.

If you install the lightning arrestor outdoors, use the supplied ground lug and a heavy wire (#6 solid copper) to connect it to a good earth ground, such as a ground rod. The connection should be as short as possible.

If you install the lightning arrestor indoors, place the wireless LAN device near a good source of ground, such as structural steel or the ground on an electrical panel. Ground the lightning arrestor by using a heavy wire (#6 solid copper) and connect the ground wire to a good ground on the structural steel or electrical panel. The connection should be as short as possible.

Review Cisco Networking for a $25 gift card