I've got a new install of CiscoWorks LMS and am getting temperature errors on my 6500 VSS. It looks like the outlet sensor is just hitting the 45C threshold.
My question is are theses default settings accurate or do I need to adjust them? The temperature in the comms room is fine and there are no performance issues.
Also is there a document with recommended temperature ranges for the components?
Thanks,
Jim
Solved! Go to Solution.
01-05-2011 03:23 AM
Jim,
Not seeing anything specific for temperature on 6500 VSS
Most cisco equipment has: Operating temperature: 32 to 104°F (0 to 40°C)
Don't think this equipment is an exception.
I would ask TAC how this can happen on multiple devices.
Cheers,
Michel
01-05-2011 02:51 AM
Could be something is blocking airflow, pager dust.
Could be a chip heating up before dying. Got a service contract?
Does cli show environment alarm threshold confirm what LMS says?
Cheers,
Michel
01-05-2011 03:05 AM
Hello,
Yeah, we have a contract but the kits new and it's happening on 2 blades on 2 different switches, so I'm not sure if this is normal.
Show env confirms thereadings are correct:
switch 1 module 9:
switch 1 module 9 power-output-fail: OK
switch 1 module 9 outlet temperature: 47C
switch 1 module 9 inlet temperature: 27C
Would like to know if there's anything published on this?
Thanks,
Jim
01-05-2011 03:23 AM
Jim,
Not seeing anything specific for temperature on 6500 VSS
Most cisco equipment has: Operating temperature: 32 to 104°F (0 to 40°C)
Don't think this equipment is an exception.
I would ask TAC how this can happen on multiple devices.
Cheers,
Michel
01-05-2011 03:25 AM
Thanks, I'll give the blades a clean then log a tac case if the problem persists.
jim