Hi, I’ve got this problem with my N7K and 2 of the fabric module’s. The front LED of the N7K is yellow/orange instead of green (it’s supposed to be green I believe). Not sure what this relates to, hw issue, config issue or?
As you can see below, 2 of the fabric module are powered down. Restarting the fab’s og restarting the N7K does not power up the fab module’s.
VDC-ADMIN# sh module
Mod Ports Module-Type Model Status
--- ----- ----------------------------------- ------------------ ----------
4 12 10/40 Gbps Ethernet Module N7K-F312FQ-25 ok
5 0 Supervisor Module-2 N7K-SUP2E active *
6 0 Supervisor Module-2 N7K-SUP2E ha-standby
7 12 10/40 Gbps Ethernet Module N7K-F312FQ-25 ok
10 4 Network Analysis Module NAM-NX1 N7K-SM-NAM-K9 ok
Mod Sw Hw
--- -------------- ------
4 6.2(6a) 1.0
5 6.2(6a) 6.0
6 6.2(6a) 6.0
7 6.2(6a) 1.0
10 6.2(6a) 1.0
Mod Application Image Description Application Image Version Status
-------- ---------------------------- ------------------------- ------
10 Application linecard image 6.0(1) ok
Mod MAC-Address(es) Serial-Num
--- -------------------------------------- ----------
4 28-34-a2-ab-e1-dc to 28-34-a2-ab-e2-17 JAE181002NA
5 e4-c7-22-10-2f-4f to e4-c7-22-10-2f-61 JAF1748AFJR
6 e4-c7-22-0f-dd-13 to e4-c7-22-0f-dd-25 JAF1748AFKG
7 54-4a-00-ac-09-d8 to 54-4a-00-ac-0a-13 JAE181002PX
10 e4-c7-22-0f-95-e6 to e4-c7-22-0f-95-ef JAF1801AABH
Mod Online Diag Status
--- ------------------
4 Pass
5 Pass
6 Pass
7 Pass
10 Pass
Xbar Ports Module-Type Model Status
--- ----- ----------------------------------- ------------------ ----------
1 0 Fabric Module 2 N7K-C7010-FAB-2 ok
2 0 Fabric Module 2 N7K-C7010-FAB-2 ok
3 0 Fabric Module 2 N7K-C7010-FAB-2 ok
4 0 Fabric Module 2 N7K-C7010-FAB-2 powered-dn
5 0 Fabric Module 2 N7K-C7010-FAB-2 powered-dn
Xbar Power-Status Reason
--- ------------ ---------------------------
4 powered-dn Reset (powered-down) because module does not boot
5 powered-dn Reset (powered-down) because module does not boot
Xbar Sw Hw
--- -------------- ------
1 NA 1.5
2 NA 1.5
3 NA 1.5
Xbar MAC-Address(es) Serial-Num
--- -------------------------------------- ----------
1 NA JAF1749AFAB
2 NA JAF1749AFDF
3 NA JAF1748AEQR
4 NA JAF1746BEFB
5 NA JAF1749AMCA
* this terminal session
VDC-ADMIN#
03-29-2014 11:29 PM
Hello,
This command might help you to know what happened.
#show environment power
Regards,
Richard
03-30-2014 01:02 PM
Well, not much info from that command.
VDC-ADMIN# sh environment power
Power Supply:
Voltage: 50 Volts
Power Actual Total
Supply Model Output Capacity Status
(Watts ) (Watts )
------- ------------------- ----------- ----------- --------------
1 N7K-AC-6.0KW 800 W 6000 W Ok
2 N7K-AC-6.0KW 641 W 6000 W Ok
3 ------------ 0 W 0 W Absent
Actual Power
Module Model Draw Allocated Status
(Watts ) (Watts )
------- ------------------- ----------- ----------- --------------
4 N7K-F312FQ-25 289 W 340 W Powered-Up
5 N7K-SUP2E 128 W 265 W Powered-Up
6 N7K-SUP2E 128 W 265 W Powered-Up
7 N7K-F312FQ-25 281 W 340 W Powered-Up
10 N7K-SM-NAM-K9 333 W 750 W Powered-Up
Xb1 N7K-C7010-FAB-2 39 W 80 W Powered-Up
Xb2 N7K-C7010-FAB-2 39 W 80 W Powered-Up
Xb3 N7K-C7010-FAB-2 44 W 80 W Powered-Up
Xb4 N7K-C7010-FAB-2 N/A 80 W Powered-Dn
Xb5 N7K-C7010-FAB-2 N/A 80 W Powered-Dn
fan1 N7K-C7010-FAN-S 198 W 720 W Powered-Up
fan2 N7K-C7010-FAN-S 198 W 720 W Powered-Up
fan3 N7K-C7010-FAN-F 14 W 120 W Powered-Up
fan4 N7K-C7010-FAN-F 14 W 120 W Powered-Up
N/A - Per module power not available
Power Usage Summary:
--------------------
Power Supply redundancy mode (configured) PS-Redundant
Power Supply redundancy mode (operational) PS-Redundant
Total Power Capacity (based on configured mode) 6000 W
Total Power of all Inputs (cumulative) 12000 W
Total Power Output (actual draw) 1441 W
Total Power Allocated (budget) 4040 W
Total Power Available for additional modules 1960 W
VDC-ADMIN#
03-30-2014 11:06 PM
Are you sure the switch hasn't been configured this way?
You can manually power down the fabics in order to minimise overall power by using the command poweroff xbar. See below:
http://www.cisco.com/c/en/us/td/docs/switches/datacenter/hw/nexus7000/installation/guide/n7k_hig_book/n7k_managing_sys_hw.html#wp1052265
03-31-2014 12:42 PM
The N7K is brand new, and the Fab mod.2 in slot 4 and 5 has been like this from the first start-up. Below is output sh module fabric 4, and attached logfile from the command no poweroff xbar 4
VDC-ADMIN# sh module fabric 4
Xbar Ports Module-Type Model Status
--- ----- ----------------------------------- ------------------ ----------
4 0 Fabric Module 2 N7K-C7010-FAB-2 powered-dn
Xbar Power-Status Reason
--- ------------ ---------------------------
4 powered-dn Reset (powered-down) because module does not boot
Xbar Sw Hw
--- -------------- ------
Xbar MAC-Address(es) Serial-Num
--- -------------------------------------- ----------
4 NA JAF1746BEFB
Chassis Ejector Support: Enabled
Ejector Status:
Left ejector CLOSE, Right ejector CLOSE, Module HW does support ejector based shutdown, Ejector policy enabled.
VDC-ADMIN#
Se attachment for output of no poweroff xbar 4.
04-30-2014 05:40 AM
Problem solved. Had to replace the N7K chassis.